View Full Version : Exhuast Fans
horsegoer
08-08-2008, 10:44 AM
I have a bunch of exhuast fans I am estimating. They show toggle switch nect to the unbit on the drawings indicated as a "St" and shown on the electrical symbol list as a motor control toggle switch. I tried looking in the spec and on the manufacturers website but don't have a clear answer. Is this a seperate switch that we mount or is it part of the unit. I was under the impression that we run power to the switch and whip to the unit but I have a feeling that is not correct.
Thanks.
jmsbrush
08-08-2008, 11:01 AM
I have a bunch of exhuast fans I am estimating. They show toggle switch nect to the unbit on the drawings indicated as a "St" and shown on the electrical symbol list as a motor control toggle switch. I tried looking in the spec and on the manufacturers website but don't have a clear answer. Is this a seperate switch that we mount or is it part of the unit. I was under the impression that we run power to the switch and whip to the unit but I have a feeling that is not correct.
Thanks.
On all the exhaust fans that we have done ,we had a disconnecting means right beside the fan, which sometimes it was just a switch
James@CHA
08-08-2008, 11:40 AM
Sounds like a motor rated switch, mounted near the equipment for disconnecting means.
horsegoer
08-08-2008, 12:20 PM
I that switch part of the unit or something we mount?
jmsbrush
08-08-2008, 12:32 PM
I that switch part of the unit or something we mount?
You are going to Install the switch, or disconnecting means. We always installed them within 5' , I'll see if i can find it in the code
jmsbrush
08-08-2008, 12:38 PM
Look at 430.102 (B) and 430.109 (2) in the 2008 NEC
sparkygriffin
08-08-2008, 12:39 PM
It is a motor starter switch. It has overloads in it which come in different sizes depending on your motors. It does not come with the fan ,you buy it.
horsegoer
08-08-2008, 03:54 PM
Thanks Very Much
infinity
08-08-2008, 04:27 PM
St means a switch with thermal overload protection. A pretty common sight on commercial jobs.
it mean switch with timer on the job im on now
Ragin Cajun
08-08-2008, 09:12 PM
SMS is how we show a manual starter with overloads. Overloads sized to motor nameplate data.
Used a lot on exhaust fans for large rest rooms, hot water circulation pumps, etc.
RC