Help would be greatly appreciated from anyone with a working understanding of tap rules. The situation is as follows:
It's a single phase residence with a 400A service. There's a fused 400 amp disconnect by the meter pedestal. Inside the home each 400A wire is spliced with a pair of 200A wires. One set goes to a 200A fused disconnect for hot water baseboard heat, the other set goes to a 200A MB distribution panel. I'm assuming the 200A wire is allowed to be fused at 400A by a tap rule. The 200A wires are under 10 feet long.
My question is:
Am I allowed another tap on this 400A wire to another 200A distribution panel if the load calculation comes in under 320A?
Dave
stickboy1375
08-09-2008, 08:02 PM
2079,,,,,,,,,,,,,,,
infinity
08-09-2008, 08:08 PM
My question is:
Am I allowed another tap on this 400A wire to another 200A distribution panel if the load calculation comes in under 320A?
Dave
Yes this is permitted. Why are you limiting yourself to 320 amps?
stickboy1375
08-09-2008, 08:09 PM
Yes this is permitted. Why are you limiting yourself to 320 amps?
80% silly, you can never use that last 20%.... :grin:
charlie
08-09-2008, 09:52 PM
80% silly, you can never use that last 20%.... :grin:HUH? 215.2(A)(1) General. Feeder conductors shall have an ampacity not less than required to supply the load as calculated in Parts III, IV, and V of Article 220. The minimum feeder-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load. ;)
Sparky555
08-09-2008, 10:48 PM
Nothing like a picture to make it clear to my dull mind.
Thanks,
Dave
infinity
08-10-2008, 12:18 AM
80% silly, you can never use that last 20%.... :grin:
The load calculation would already include 125% so your permitted calculated load is 400 amps.
stickboy1375
08-10-2008, 10:17 AM
The load calculation would already include 125% so your permitted calculated load is 400 amps.
I know, I guess that smiley wasnt enough....
charlie
08-10-2008, 10:56 AM
I know, I guess that smiley wasn't enough....
It was but it could be misleading to a lot of inexperienced electricians who just read the posts and are just starting out. :)
stickboy1375
08-10-2008, 11:02 AM
It was but it could be misleading to a lot of inexperienced electricians who just read the posts and are just starting out. :)
Yeah, sometimes my mouth is faster than my brain... :grin: