View Full Version : Min size wire from meter
bth0mas20
08-09-2008, 11:56 PM
I need to install a meter from the power company and feed only a well pump.
Is their a min code for the size of wire that I can feed from the power meter to the main breaker panel that will be inside the shed 7ft away from the shed?
mdshunk
08-10-2008, 12:16 AM
Yes, and that wire size is dictated in large part by the chart that shows the acceptable gauges for the terminals on the load side of the meter can.
Dennis Alwon
08-10-2008, 08:11 AM
I had not thought of what Marc has mention but also take a look at 230.79.
230.79 Rating of Service Disconnecting Means.
The service disconnecting means shall have a rating not less than the calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable. In no case shall the rating be lower than specified in 230.79(A), (B), (C), or (D).
(A) One-Circuit Installations. For installations to supply only limited loads of a single branch circuit, the service disconnecting means shall have a rating of not less than 15 amperes.
(B) Two-Circuit Installations. For installations consisting of not more than two 2-wire branch circuits, the service disconnecting means shall have a rating of not less than 30 amperes.
(C) One-Family Dwellings. For a one-family dwelling, the service disconnecting means shall have a rating of not less than 100 amperes, 3-wire.
(D) All Others. For all other installations, the service disconnecting means shall have a rating of not less than 60 amperes.
iwire
08-10-2008, 08:31 AM
I had not thought of what Marc has mention but also take a look at 230.79.
230.79 has little to no impact on conductor sizes, only the size of the disconnecting means.
augie47
08-10-2008, 09:01 AM
Yes, and that wire size is dictated in large part by the chart that shows the acceptable gauges for the terminals on the load side of the meter can.
That's certainly the situation in this area. We have a lot of Cable TV service boxs with a SP 15 OCP and a #4 (socket minimum) service wire.
cschmid
08-10-2008, 09:38 AM
I believe the poco determine minimum meter sizes as well
ElectricianJeff
08-10-2008, 09:40 AM
That's certainly the situation in this area. We have a lot of Cable TV service boxs with a SP 15 OCP and a #4 (socket minimum) service wire.
I recently replaced the service to the lighted entrance to a older subdivision here in town. The existing 2 circut load was connected with #12 thwn from the meter. The service entrance conductors where #12 also underground from the pole located about 10' away and 15' up.
I calculated the total load at less than 12 amps and upped the wire to #10 and protected it at 20 amps. No inspection was required and the POCO reconnected it with no questions.
Where would I find the "socket minimum" of a metercan? It didn't "feel" right at the time putting the #10 under the lugs of that 100 amp. can.
augie47
08-10-2008, 10:08 AM
I recently replaced the service to the lighted entrance to a older subdivision here in town. The existing 2 circut load was connected with #12 thwn from the meter. The service entrance conductors where #12 also underground from the pole located about 10' away and 15' up.
I calculated the total load at less than 12 amps and upped the wire to #10 and protected it at 20 amps. No inspection was required and the POCO reconnected it with no questions.
Where would I find the "socket minimum" of a metercan? It didn't "feel" right at the time putting the #10 under the lugs of that 100 amp. can.
I have normally found the wire sizes listed on a sticker in the meter socket.
If not, you should be able to find them from the mfg..
For example:
http://www.milbankmfg.com/Products/Catalogs/CatalogFiles/PDF/REC.pdf
ElectricianJeff
08-10-2008, 10:18 AM
Thanks for the link, Gus
The can was old but still served the purpose. The sticker was long since readable.
I used the logic that if the POCO ran #12 on the line side than they would love my #10 on load side.:smile: But it just didn't feel right at the time.
mdshunk
08-10-2008, 10:24 AM
I used the logic that if the POCO ran #12 on the line side than they would love my #10 on load side.:smile: But it just didn't feel right at the time.Yeah, I've seen that a few times on some of the older billboards I work on. They'd normally skin the conductor three times too long, then fold it over three times to make it thicker for the lug. Not right, but better than a single #12 or #10.
bth0mas20
08-10-2008, 10:38 AM
Thanks for your help I will keep you posted
ElectricianJeff
08-10-2008, 10:53 AM
Yeah, I've seen that a few times on some of the older billboards I work on. They'd normally skin the conductor three times too long, then fold it over three times to make it thicker for the lug. Not right, but better than a single #12 or #10.
I've never worked on a billboard but did the same thing. I wanted to have a little more meat under that lug.
Buck Parrish
08-10-2008, 01:55 PM
I need to install a meter from the power company and feed only a well pump.
Is their a min code for the size of wire that I can feed from the power meter to the main breaker panel that will be inside the shed 7ft away from the shed?
Also when chooseing your wire size. If you have a submergible pump. Factor in the depth of your well.
charlie
08-10-2008, 02:09 PM
. . . They'd normally skin the conductor three times too long, then fold it over three times to make it thicker for the lug. Not right, but better than a single #12 or #10.
I think you are correct but what is the code section that was violated? It is just a single conductor so is this a violation of the intent of the code (I don't think 110.14(A) is violated)? Is it a violation of "workmanlike" in section 110.12? Perhaps a violation that 90.4 can handle although, in my opinion, the AHJ should never use this section. :-?
mdshunk
08-10-2008, 02:17 PM
I think you are correct but what is the code section that was violated? 110.3(B). A 100 amp meter can, for instance, normally lists #6 as the smallest permissible conductor. A #12, no matter if it's folded over enough times to be as thick as a #6, is still a #12 conductor.
charlie
08-10-2008, 02:22 PM
HMMMM, OK. http://forums.mikeholt.com/images/icons/icon11.gif
nakulak
08-10-2008, 04:06 PM
I think you are correct but what is the code section that was violated? It is just a single conductor so is this a violation of the intent of the code (I don't think 110.14(A) is violated)? Is it a violation of "workmanlike" in section 110.12? Perhaps a violation that 90.4 can handle although, in my opinion, the AHJ should never use this section. :-?
I wholeheartedly disagree. I believe that article 90 should be strictly enforced, and I look forward to the day I can receive a violation listing that article.