View Full Version : Sharing Neutrals, Isolated Grounds etc.
horsegoer
09-07-2008, 10:01 AM
This is where I get a bit confused when estimating. I was told if it is a normal 20A circuit I can us 5 wires per 3 circuits. Hot per circuit and share a ground & neutral for the three? Now If have isolated ground receptacles I need a separate ground wire for each circuit??????? So if I am running out a 6 circuit home run and 3 of those circuits are isolated grounds how many wires would I be running out to my HR box? 12? 5 for the 3 reg circuits and 7 for the iso grounds......1 hot & 1 ground per iso circuit and share the neutral makes 7 for the 3 iso circuits.
The amount wire for circuits screws me up.
Smart $
09-07-2008, 10:52 AM
Much of how many wires you run is a design decision. Out of a 3Ø 4W panelboard you could run 3 "convenience" circuits and 3 "isolated" circuits in one conduit as:
Minimum wires — 6 ungrounded, 2 grounded, 1 grounding, 1 isolated grounding
or
Maximum wires — 6 ungrounded, 6 grounded, 6 grounding, 3 isolated grounding.
How many do you want to run?
Sparky555
09-07-2008, 11:38 AM
Sorry I'm not following your question very well, but I'll try to explain. I rarely run isolated grounds, but by definition I suspect that means an insulated green wire per circuit. A std. circuit is 2 wire (1 grounded, 1 ungrounded). A shared neutral circuit (two circuits) is 3 wire (1 grounded, 2 ungrounded). If you don't know the proper way to terminate them on the circuit breakers, don't do shared neutrals. It creates a fire hazard. When I run multiple shared neutral circuits in the same conduit I use different color wires to keep them straight. Figure out how many circuits you need & run 2 or 3 wire circuits. In conduit you have to derate above 9 current-carrying conductors. This is all for 1 PH. It's different for 3 PH.
Dave
infinity
09-07-2008, 11:41 AM
Sparky, could you please explain how shared neutrals are a fire hazard?
iwire
09-07-2008, 11:46 AM
but by definition I suspect that means an insulated green wire per circuit.
Dave, as Smart pointed out the above is a up to the designer, an IG setup might require one IG conductor per outlet, one IG per circuit, or one IG for multiple circuits.
The IGs rarely run separately all the way back to the bonding point which is typically XO at the transformer.
Often the way I see it is one IG and one EGC per raceway or cable no mater how many circuits they serve. Once they reach the panel the IGs are landed on a isolated grounding bar and a single IG conductor is run from that bar all the way back to XO at the transformer supplying that panel.
infinity
09-07-2008, 11:48 AM
Dave, as Smart pointed out the above is a up to the designer, an IG setup might require one IG conductor per outlet, one IG per circuit, or one IG for multiple circuits.
The IGs rarely run separately all the way back to the bonding point which is typically XO at the transformer.
Often the way I see it is one IG and one EGC per raceway or cable no mater how many circuits they serve. Once they reach the panel the IGs are landed on a isolated grounding bar and a single IG conductor is run from that bar all the way back to XO at the transformer supplying that panel.
I agree, one EGC and IG shared per raceway is adequate. Separate EGC's and IG's are a waste of money.
iwire
09-07-2008, 11:51 AM
I agree, one EGC and IG shared per raceway is adequate. Separate EGC's and IG's are a waste of money.
Like IGs aren't a waste anyway? :D
Sparky555
09-07-2008, 12:08 PM
Sparky, could you please explain how shared neutrals are a fire hazard?
In 1 PH terminating both circuits on the same leg makes the current additional instead of subtractive. That can put to much current through the grounded conductor unless you size it accordingly.
Dave
LarryFine
09-07-2008, 03:51 PM
So if I am running out a 6 circuit home run and 3 of those circuits are isolated grounds how many wires would I be running out to my HR box?Here's my calc:
3) ckts can be standard 3p MWBC, so that's 5: 3 hots, 1 neutral, one EGC (or if you use conduit, make it 4)
3) 2-wire ckts w' individual neutrals and IG's, makes 9: 3 hots, 3 neutrals, 3 IG's (use the EGC/conduit above)
That makes a total of 14, or 13 if the raceway is the EGC.
LarryFine
09-07-2008, 03:57 PM
Sparky, could you please explain how shared neutrals are a fire hazard?I believe the correct statement is that improperly-wired circuits using shared neutrals can be a hazard.
TOOL_5150
09-07-2008, 05:29 PM
Like IGs aren't a waste anyway? :D
Not completly useless Bob. I worked as a field tech for 2 years working on nortel meridian phone systems. The systems call for an isolated ground all the way back to XO on the transformer, and it had to be a #6 copper wire. There was a problem with this one particular switch [PBX]. It would keep restarting. They take a few minutes to come completly back up, so out of a huge building with thousands of people using the phone syatem... they notice when its down. Come to find out, we had a bootleg ground that was tied to building steel. The senior tech I was with said that was the problem... it was routed back to the transformer and they no longer had the weird random restarts.
I would not have believed it unless I saw it myself. But an IG fixed that problem.
~Matt
iwire
09-07-2008, 05:52 PM
I would not have believed it unless I saw it myself. But an IG fixed that problem.
~Matt
I am willing to bet other ways would have fixed it as well. The real problem in my mind with IGs is that in most all installations it will be compromised by some incidental contact with a non isolated ground.
Better in my mind to design the system to work properly without IGs so that it will continue to work. :smile:
mattsilkwood
09-07-2008, 06:31 PM
Like IGs aren't a waste anyway? :Di couldnt argee more a ground is a ground is a ground.
back to the op i argee with the others that its up to the designer as to how the ig is to be installed. just install to the specs and cya
TOOL_5150
09-07-2008, 06:47 PM
I am willing to bet other ways would have fixed it as well. The real problem in my mind with IGs is that in most all installations it will be compromised by some incidental contact with a non isolated ground.
Better in my mind to design the system to work properly without IGs so that it will continue to work. :smile:
THis is very true. I still dont know why a multi-thousand dollar PBX couldnt handle a little bit of interference. Last time I talked to someone about an IG circuit, they tied the box to the EGC and the IG terminal on the recep to a ground rod. :-? :roll:
~Matt
DLTravis
09-08-2008, 04:29 PM
Sparky, could you please explain how shared neutrals are a fire hazard?
I know you asked Sparky but I would like to chime in :roll: . As a note, I love MWBC's. BUT.....
If they are not installed with care they can be hazardous.
I recently had a problem where a table lamp and a computer let out their beloved smoke (fire hazard).
In this case the original installer used questionable connection points (i.e. terminal blocks with four wires terminated on one side). The Neutral opened from the panel but the other three neutral connections stayed connected (three phase 120/208 panel). If I was smarter I'd post a drawing of how this looks but it puts 208 VAC across a series of 120 VAC loads. This might not cause problems if you have exactly equal loads but a table lamp and a desktop PC do not have equal resistances (impedance). The light did not last long - once it opened all was good in the electron world but it was too late for our keyboarded friend - he gave his life in the fight :grin: The third phase was not being used at the time.
Granted the installer was in violation with his termination choice. At least I think he was, I never was able to find the listing for the type of terminal strips he used. But this could happen with a wire nut or any other type of device intended to terminate (4) #12 wires.
While I love and use MWBC's and will continue to use them. They do present a unique hazard when things go wrong.:cool:
Thanks for listening, er, I mean reading
Travis
iwire
09-08-2008, 04:43 PM
So what your saying is poor electrical installation practices are hazardous .... that is not limited to MWBCs.
DLTravis
09-08-2008, 04:52 PM
So what your saying is poor electrical installation practices are hazardous .... that is not limited to MWBCs.
True, but there are things other than poor wiring practices which cause wires to open. To deny that MWBC's pose unique hazards is illogical. To propose they not be used because of these hazards is foolish.
LarryFine
09-08-2008, 05:15 PM
True, but there are things other than poor wiring practices which cause wires to open. To deny that MWBC's pose unique hazards is illogical. To propose they not be used because of these hazards is foolish.DL, keep in mind that services themselves are basically MWBC's. Many times has an open neutral caused destructive voltage imbalances. They are not limited to branch circuits.
iwire
09-08-2008, 05:43 PM
To deny that MWBC's pose unique hazards is illogical.
Installed per NEC rules I see no additional hazard, as Larry mentions essentially all circuits are supplied via a shared neutral.
DLTravis
09-09-2008, 09:18 AM
Installed per NEC rules I see no additional hazard, as Larry mentions essentially all circuits are supplied via a shared neutral.
DL, keep in mind that services themselves are basically MWBC's. Many times has an open neutral caused destructive voltage imbalances. They are not limited to branch circuits.
Here's where I disagree:
What would have happened in this same situation (open neutral) had this not been a MWBC?
Answer:
Devices would have lost power - smoke stays where it belongs.
Simple as that.;)
iwire
09-09-2008, 10:21 AM
Here's where I disagree:
What would have happened in this same situation (open neutral) had this not been a MWBC?
Which is a direct result of bad installation techniques, not the MWBC.
We will remain in disagreement. :)
LarryFine
09-09-2008, 11:43 AM
Here's where I disagree:
What would have happened in this same situation (open neutral) had this not been a MWBC?
Answer:
Devices would have lost power - smoke stays where it belongs.
Simple as that.;)
Question: And what would occur if the same thing happened to your service where you live?
Answer: The same thing. Have you requested that your POCO run two grounded conductors to your house?
gregldoyle
09-25-2008, 02:38 PM
Hi, new to the forum.
I design broadcast and av systems and many of my clients request iso grounds. This is due to the extremely low-level audio signals and ground differential between distant locations across a facility. Differential hum is a killer for microphone level audio. Also a problem for digital audio and video where it causes bit errors when connecting two points together with different ground potentials. We design the systems with "floating" racks and bond the iso ground to the equipment racks. I see two definitions for this, iso-ground and enhanced ground. For most installations, I agree, isolated grounds are a waste of good (and expensive) copper. For some technical installations, it's worth it.
Greg D.
Senior Designer
Black Diamond, WA
Greg1707
09-25-2008, 06:29 PM
Since we are on this subject here is my question. I have a panel and six feet above the panel in the attic I have a jbox. The jbox is connected to the panel by conduit. I want to run multiple 120v circuits to this jbox from the panel. From the jbox I will split off to multiple home runs. Assuming that I will not be using MWBC how many neutrals do I need? I assume that I can just use one neutral as long as it is sized correctly? If this is correct do I size it according to the calculated combined load of the circuits?
bradleyelectric
09-25-2008, 09:41 PM
Since we are on this subject here is my question. I have a panel and six feet above the panel in the attic I have a jbox. The jbox is connected to the panel by conduit. I want to run multiple 120v circuits to this jbox from the panel. From the jbox I will split off to multiple home runs. Assuming that I will not be using MWBC how many neutrals do I need? I assume that I can just use one neutral as long as it is sized correctly? If this is correct do I size it according to the calculated combined load of the circuits?
How can you be a master electrician, an aspiring electrician and not know the answer to this question all at the same time?
LarryFine
09-26-2008, 01:16 AM
How can you be a master electrician, an aspiring electrician and not know the answer to this question all at the same time?I'd be happy just knowing about the first two! :-?
Greg1707
09-26-2008, 07:51 AM
How can you be a master electrician, an aspiring electrician and not know the answer to this question all at the same time?
First of all thanks for your quick response. I have virtually no experience working with conduit or FMC. The electrical field quite large, as you know from reading this forum. The field encompasses installing ceiing fans all the way to wiring industrial plants. Most of us make a career out of just working in one little area of the field. I am not very experienced in many areas and appreciate this forum to learn more.
So to repeat the question. Can I run 6 120 volt #12 THHN ungrounded conductors from the panel using FMC to a large junction box and run only one properly sized neutral conductor to the junction box. At the junction box the THHN would be spliced to 6 #12 romex cables. The properly sized neutral would be spliced to the 6 romex cables as well. All conductors of the circuits are in the same cable and raceway.
steelersman
11-15-2008, 04:51 PM
Can I run 6 120 volt #12 THHN ungrounded conductors from the panel using FMC to a large junction box and run only one properly sized neutral conductor to the junction box. At the junction box the THHN would be spliced to 6 #12 romex cables. The properly sized neutral would be spliced to the 6 romex cables as well. All conductors of the circuits are in the same cable and raceway.
You would need 3 neutral conductors. You can share 2 circuits per neutral, assuming the service is 120/240 single phase. Just make sure that each pair of circuits that share a neutral are on seperate legs, ot on the same leg. Also you don't need to upsize your neutrals as long as you do as I said above. 3 #12 neutrals would cover the six #12 120 volt circuits.