I have a job coming up that consists of wiring a 12kw floor heat boiler. The only specs from the manufacturer are to use a 70 amp breaker and copper conductors only. It is in a newer house where the ceilings are not yet finished and it is located 40 feet from the panel. My question is do they make a nm cable this large (#4 awg) or will I have to pipe it. Thanks in advance.
walkerj
10-05-2008, 04:49 PM
Yes they make cable #4 and larger
480sparky
10-05-2008, 04:49 PM
You can use ser cable (the gray stuff).
I'd submit an RFI for more information.
Dennis Alwon
10-05-2008, 04:49 PM
I have a job coming up that consists of wiring a 12kw floor heat boiler. The only specs from the manufacturer are to use a 70 amp breaker and copper conductors only. It is in a newer house where the ceilings are not yet finished and it is located 40 feet from the panel. My question is do they make a nm cable this large (#4 awg) or will I have to pipe it. Thanks in advance.
Yes they make NM up to #2 copper in NM but they also make ser copper larger than that.
iwire
10-05-2008, 04:50 PM
I suggest running aluminum SE or SER.
walkerj
10-05-2008, 04:51 PM
I suggest running aluminum SE or SER.
I like the way you think!:D
Dennis Alwon
10-05-2008, 04:56 PM
I suggest running aluminum SE or SER.
Even if the spec require copper? Never mind you are probably talking about the feeder not the wire to the heater.
iwire
10-05-2008, 05:00 PM
Even if the spec require copper?
Well yes, you know me, ignore the rules and save a dime. :grin:
Almost everything I install has dual rated lugs, if I was in a pinch I could install pin adapters on the aluminum to deal with a copper only termination.