10-10-2008, 07:19 AM
had an inspector turn me down because I used a standerd knockuot seal(push penny) in a 200 amp nema three panel. The knockout I closed was one of the concentric ones at the bottom sides. My memory is that all entries below energized parts in a nema 3 enclosure do not have to be sealed. My NEC on CD took a dive and I am needing a code article on this one . Also where is the cheapest place to order a new CD.
walkerj
10-10-2008, 07:50 AM
I don't see a problem with the install.
They do make a knockout seal that has a gasket and screws in to make it watertight.
http://www.necplus.org
billsnuff
10-10-2008, 08:24 AM
408.7 unused openings
312.2(A) damp, wet locations
05 nec
masterinbama
10-10-2008, 08:29 AM
Thanks for the replies I will call the inspector first thing. He is a good sport when it comes to calling him on code issues, like all of us he continues to learn.
. He is a good sport when it comes to calling him on code issues, like all of us he continues to learn.
Sounds like a good guy.:smile:
masterinbama
10-10-2008, 09:28 AM
He is I started in this trade working for his dad way back when 1980. So I have known him for a year or two.
cadpoint
10-10-2008, 10:00 AM
He is I started in this trade working for his dad way back when 1980. So I have known him for a year or two.
You meant a decade or two, right ? :grin:
Two questions : Whats your re-inspection fee if any?
I know that your town is sudo isolated by its location, granted the work slow-down effected you as well, or has it?
Seems to me there's been a large influx of white collar job's and the odd assortment of Big Name Company's in your region and buffering ya'll like other regions that have a deverse amount of employers.
LarryFine
10-10-2008, 12:50 PM
Whats your re-inspection fee if any?I find it hard to believe you'd have to pay for a re-inspection for a wrong call by the inspector.
roger
10-10-2008, 01:19 PM
I find it hard to believe you'd have to pay for a re-inspection for a wrong call by the inspector.
So do I
Roger
cadpoint
10-10-2008, 01:30 PM
I find it hard to believe you'd have to pay for a re-inspection for a wrong call by the inspector.
Gezz wally,:grin: First this is a nema three panel, is a coin suffient for this ?
Matching or like construction keeps tumbling in my mind...
All opening are to be suffently closed is also in the mix.
As I recall a member here posted some UL statements on coins and stated that a coin will not be, to say, up to snuff in all cases.
roger
10-10-2008, 01:41 PM
Gezz wally,:grin: First this is a nema three panel, is a coin suffient for this ?
Yes it is.
Would you use a Meyers Hub for entering into the bottom of this panel?
Roger
360Youth
10-10-2008, 01:53 PM
Also where is the cheapest place to order a new CD.
This (http://cgi.ebay.com/National-Electrical-Code-2008-on-CD-Rom_W0QQitemZ380070380954QQihZ025QQcategoryZ2228QQ rdZ1QQssPageNameZWD1VQQcmdZViewItemQQ_trksidZp1638 Q2em118Q2el1247) is probably where I will start looking when I eventually get one.
cadpoint
10-10-2008, 02:32 PM
Yes, Good, OK, Granted as most all things are rated in some way or another. I will admit that NEMA applications are not exactly at my fingers tips or in my mind as to when, where, why.
I just have to take care as an installer when I deal with a "NEMA" rated device. My thinking here will be I have to do a little more or something extra, or genrally have some higher level of "Pay Attention".
Frankly maybe just the four letter word starts the tumblers.
Ok to expand on the Thread/Question why a NEMA 3 verses a NEMA 1. Is this due to type of service and the type of conditions around this service point? I don't think that this is was clearly presented.
The OP's thought expressed what he beleived was the default of the inspection, he doesn't have a book handy and their CD went south.
Posted in the AM and possiably in a hurry? I don't know! But it reassuring to come here and post and run around all day and know someone might/will have said something!
I hope Meyer made as much money as colorado slim did, but then that not the point! :)
nolabama
10-10-2008, 04:03 PM
put a myers hub and a plug and go to the next one
bradleyelectric
10-10-2008, 04:07 PM
Ok to expand on the Thread/Question why a NEMA 3 verses a NEMA 1. Is this due to type of service and the type of conditions around this service point? I don't think that this is was clearly presented. :)
NEMA 1 is standard indoor environment NEMA 3R is wet location to simplify types. there are others
roger
10-10-2008, 04:20 PM
put a myers hub and a plug and go to the next one
That would be up to you if you wanted to spend the money, but it's not necessary.
Roger
LarryFine
10-10-2008, 08:38 PM
First this is a nema three panel, is a coin suffient for this ?I'd say so. Are factory-punched KO's any more raintight?
I'd say so. Are factory-punched KO's any more raintight?
yea 3r's get an extra coat of paint
LarryFine
10-11-2008, 01:12 AM
yea 3r's get an extra coat of paintMaybe so, but they still have holes at the bottom corners to allow water to drain.
masterinbama
10-11-2008, 07:31 AM
You meant a decade or two, right ? :grin:
Two questions : Whats your re-inspection fee if any?
I know that your town is sudo isolated by its location, granted the work slow-down effected you as well, or has it?
Seems to me there's been a large influx of white collar job's and the odd assortment of Big Name Company's in your region and buffering ya'll like other regions that have a deverse amount of employers.
We are somewhat isolated as far as swings in the economy. Are main employer here is the DOD and NASA but we also have our fair share of manufacturing. International Diesel built a plant here and so did Toyota Motor manufacturing. What is keeping us going right now is the Governments Base Realignment And Closure Committee. We stand to get 25,000 government jobs here in the next 4 years.
jrannis
10-11-2008, 08:22 AM
had an inspector turn me down because I used a standerd knockuot seal(push penny) in a 200 amp nema three panel. The knockout I closed was one of the concentric ones at the bottom sides. My memory is that all entries below energized parts in a nema 3 enclosure do not have to be sealed. .One Word comes to mind "Duct Tape":grin:
billsnuff
10-11-2008, 09:03 AM
http://media.canada.com/canwest/143/rgreen.jpg
masterinbama
10-11-2008, 11:32 AM
http://media.canada.com/canwest/143/rgreen.jpg
Didn't think duct tape worked to well in Hawkeye country. Never the less go Hawkeyes beat Indiana!
hardworkingstiff
10-11-2008, 11:41 PM
That would be up to you if you wanted to spend the money, but it's not necessary.
Roger
And you will have to do it from now on.
billsnuff
10-12-2008, 08:23 AM
Didn't think duct tape worked to well in Hawkeye country. Never the less go Hawkeyes beat Indiana!
45-9 go hawks