Was in looking at a potential new client, and it's basically an electronics manufacturer - PC board type. What was scattered aroudn the facility was drops that consisted of SO cord with a quad receptacle configuration at the bottom. There were stress relief (Chinese finger type) at the portion coming through the ceiling and also stress relief at the box end.
What code section would cover this? I find it hard to consider this permanent wiring, but we know that it is. They want more of this, but I'm really leaning towards just running EMT on the walls. When I asked the maintenance guy what the thought was behind the cord drops - he indicated that the previous EC indicated it was "cheaper" for them to just have him run these drops. Maybe he didn't own an EMT bender.
stickboy1375
10-10-2008, 07:43 PM
There were stress relief (Chinese finger type) at the portion coming through the ceiling and also stress relief at the box end.
So was the SO actually run through a ceiling? or to a box mounted to the ceiling?
mattsilkwood
10-10-2008, 08:17 PM
i see this in alot of industrial apps. mainly where they move equipment around alot. but normally i see a single cord end, but as long as you use a bell box (threaded ko) and a kellum grip i dont see a problem with it.
bjp_ne_elec
10-10-2008, 08:17 PM
SO is going up into the ceiling.
mattsilkwood
10-10-2008, 08:21 PM
i missed the part were it was going through a ceiling. that might change things. are these out in the middle of the floor or along the wall.
bjp_ne_elec
10-10-2008, 08:28 PM
They tend to be about a foot off the wall. Then the maintenance guy said they wanted him to affix them to some of the solder workstations they're dropped down to. Now we're really talking permanent.
I know you can't have an outlet up in the ceiling and have a cord running to that. I know I went in one office facility, and that's how their "handyman" wired up all the projectors they had hung from the ceiling in their Conference rooms.
box offset
10-10-2008, 08:51 PM
SO cord drops are common in most of are industrial accounts. As long as they have kellum grips at both ends. If the quads are in a appleton(bell) box with threaded KO's thats the norm in my area. :smile:
benaround
10-10-2008, 09:28 PM
i see this in alot of industrial apps. mainly where they move equipment around alot. but normally i see a single cord end, but as long as you use a bell box (threaded ko) and a kellum grip i dont see a problem with it.
matt, as far as the NEC 314.23(H)(1) the box needs to have threaded 'hubs'
a bell box with threaded ko's would not be considered as 'hubs'.
With that said, some areas may allow 'bell boxes'.
matt, as far as the NEC 314.23(H)(1) the box needs to have threaded 'hubs'
a bell box with threaded ko's would not be considered as 'hubs'.
With that said, some areas may allow 'bell boxes'.
I sometimes use suspended receptacles or drops to machinery, on extra-heavy duty cord w/ strain relief is it's in the middle of a manufacturing area but it's hard to justify the extra costs over EMT, along a wall.
wireguru
10-10-2008, 10:55 PM
you could also use these http://www.woodhead.com/data/current1488/multiple%20outlet%20boxes%20902.pdf
benaround
10-10-2008, 11:22 PM
you could also use these http://www.woodhead.com/data/current1488/multiple%20outlet%20boxes%20902.pdf
That's what We normally use, and you can see the 'hubs' on those also.
mattsilkwood
10-11-2008, 10:33 AM
wouldnt a bell box be considered a threaded hub?
steved
10-11-2008, 01:51 PM
It seems to be pretty much standard around here to just use a 1900 box on the end of the SO cord drop, usually with just a Romex connector to secure the cord to the box. I've seen this kind of setup in every factory I've worked in.