View Full Version : Copper Pipe Turns Green
grant
11-06-2008, 07:00 PM
Have a customer who called because the copper water pipes in his house have turned green. Without getting into all that I found there was current traveling on the copper pipes. I have corrected that condition. Has anyone seen this happen and will the green slowly go away now that the current has been removed? Not sure if the current flow turns copper pipe green.
mdshunk
11-06-2008, 07:03 PM
The green pipe has nothing to do with the fact that current was flowing on the pipe.
charlie b
11-06-2008, 07:09 PM
The "Material Sciences" course that I was required to take in college was not my best friend, so I have very few facts to offer. I do know that when copper rusts, it turns green. What I do not know is whether current flowing through a section of copper can accelerate the rate of corrosion.
Were you able to detect and measure the current flowing in the pipe? Did it make the pipe feel hot to the touch? I believe that higher temperatures will accelerate the rate of corrosion.
jjhoward
11-06-2008, 07:10 PM
I have been told that the phone company calls the DC current on their phone lines "sealing current". This is to help keep the copper to copper connections connected??
So maybe that current was keeping all that plumbing together.
dereckbc
11-06-2008, 07:18 PM
It has nothing to do with current, it is a reaction from air and moisture called patina.
Initially, bare Cu metal atoms react with air to form the pink oxide, cuprite, Cu2O, which has Cu+1 cations. This gradually oxidizes further to the black oxide, tenorite, CuO, with Cu+2 ions. The black sulfide CuS also sometimes forms. In the presence of moisture, the blackish layer slowly reacts with sulfur dioxide and carbon dioxide from the air to eventually form the patina, which is a mixture of 3 minerals:
brochantite, a green, hydrated copper sulfate, Cu4SO4(OH)6
malachite, the green, hydrated copper carbonate Cu2CO3(OH)3
azurite, the blue, hydrated copper carbonate Cu3(CO3)2(OH)2
In these compounds, copper atoms from the metal surface have been fully oxidized into Cu+2 (cupric) ions. The rate of patina formation and the proportion of the components depend upon humidity and the amount of air pollution.
480sparky
11-06-2008, 07:22 PM
So how much current is required to make a copper roof turn green?:confused:
http://i214.photobucket.com/albums/cc172/480sparky/copperroof.jpg
jjhoward
11-06-2008, 07:24 PM
Geez Dereckbc; Were you just waiting for that question??
Thank you for trip down memory lane to physics class!
I hope there won't be a pop quiz.
wptski
11-06-2008, 07:26 PM
Okay, why would have one single wire going to a breaker box full of other breakers turn green?:confused:
chris kennedy
11-06-2008, 07:28 PM
Okay, why would have one single wire going to a breaker box full of other breakers turn green?:confused:
It always wanted to be an EGC?
Dennis Alwon
11-06-2008, 07:33 PM
Okay, why would have one single wire going to a breaker box full of other breakers turn green?:confused:
I have seen this happen. In my case the bare wire was next to the panel feed close to it's termination. The connection was loose and the jacket on the wire started melting and the bare copper wire had formed into the conductors insulation but had not shorted out (yet). The green color formed right where the bare conductor was almost touching the feeder.
weressl
11-06-2008, 07:35 PM
The "Material Sciences" course that I was required to take in college was not my best friend, so I have very few facts to offer. I do know that when copper rusts, it turns green. What I do not know is whether current flowing through a section of copper can accelerate the rate of corrosion.
Were you able to detect and measure the current flowing in the pipe? Did it make the pipe feel hot to the touch? I believe that higher temperatures will accelerate the rate of corrosion.
'Corrosion' in the colloquial use is nothing else but an electrochemical reaction between two electrogalvanically dissimilar metal or metallic compound. Most common metallic compound is salt that is freely present all around as.
Any natural corrosion can be accelerated by the introduction of a potential differential. Have a potential differential and a conductive path and there is your completed circuit with the above detected 'current flow'.
Sometimes this current flow is intentionally induced to protect undergound metallic objects. This is called cathodic protection. The 'greening' of a copper pipe sure can be a sign of stray current and left alone long enough will create a piping failure.
It has nothing to do with current, it is a reaction from air and moisture called patina.
Initially, bare Cu metal atoms react with air to form the pink oxide, cuprite, Cu2O, which has Cu+1 cations. This gradually oxidizes further to the black oxide, tenorite, CuO, with Cu+2 ions. The black sulfide CuS also sometimes forms. In the presence of moisture, the blackish layer slowly reacts with sulfur dioxide and carbon dioxide from the air to eventually form the patina, which is a mixture of 3 minerals:
brochantite, a green, hydrated copper sulfate, Cu4SO4(OH)6
malachite, the green, hydrated copper carbonate Cu2CO3(OH)3
azurite, the blue, hydrated copper carbonate Cu3(CO3)2(OH)2
In these compounds, copper atoms from the metal surface have been fully oxidized into Cu+2 (cupric) ions. The rate of patina formation and the proportion of the components depend upon humidity and the amount of air pollution.
Correct but current flow will accelerate the process.
dereckbc
11-06-2008, 09:13 PM
Correct but current flow will accelerate the process.
DC current will but not AC current.
Weressi touched on one effect telephone company's uses or at least to use. Telephone battery plants use a positive ground reference. In the old days outside plant cables use to be lead sheathed. By referencing the positive terminal of the battery set up Cathodic Protection of the cables. By referencing the positive terminal instead of corrosion you actually build minerals around the cable. If you referenced the negative terminal to ground you would accelerate corrosion. CP does not work with AC.
Now with that said one known problem in telephone offices with battery plants is copper and steel pipes degrading which is seen as small pin holes and leaks. This is from DC current flowing in the structure.
The only way I know of for AC to have any effect on copper is if there is a difference of potential between two dissimilar metals like Aluminum contacting Copper.
iwire
11-06-2008, 09:17 PM
Lets define the current flow we are talking about.
It seems obvious to me the current flow from one end of a copper pipe to the other will not promote the greening of the pipe, if that was the case all our conductors would be green.
On the other hand a copper pipe buried in the dirt with current flow between the pipe and the dirt it is contact with may accelerate the process.
dereckbc
11-06-2008, 09:34 PM
From Copper.org
Recently I purchased sheets of copper and would like to know what I can put on the copper to prevent it from turning green or looking like an old penny. Can you tell me what product I should use to protect my copper countertops as well as the copper sheet behind my range?
One reservation you may have about copper is the material's tendency to turn green with age. Contrary to popular belief, this oxidation only occurs when the copper is directly exposed to outdoor elements or acidic conditions.
dereckbc
11-06-2008, 09:48 PM
One more thought. Is there any galvanised clamps, fittings, or even a nail touching the copper any where? Just a single nail touching a copper line will cause a reaction. I know plumbers that have had to re-pipe whole homes from galvanized fittings being used.
wptski
11-06-2008, 11:51 PM
I have seen this happen. In my case the bare wire was next to the panel feed close to it's termination. The connection was loose and the jacket on the wire started melting and the bare copper wire had formed into the conductors insulation but had not shorted out (yet). The green color formed right where the bare conductor was almost touching the feeder.
In my case, it was just one hot wire to one of the breakers. The entire end where the insulation was stripped was green except where the screw made contact. It was tight too.
weressl
11-07-2008, 11:07 AM
DC current will but not AC current.
Theoretically this is correct. In practice the natural surrounding contains elements that DO act as semiconductors or diodes, so there is a small amount of the AC that leakes as DC. Not to mention the DC component that exist during arcing switching.
dereckbc
11-07-2008, 03:34 PM
Theoretically this is correct. In practice the natural surrounding contains elements that DO act as semiconductors or diodes, so there is a small amount of the AC that leakes as DC. Not to mention the DC component that exist during arcing switching.
I agree with you but; DC (AC for that matter) current alone will not turn copper green or black. It takes a chemical or galvanic reaction to turn copper green or black. DC current can accelerate the process, but not cause the reaction. The root cause of the problem is chemical, not current.
My best guess is this is an enviromental condition like moisture (sweating/condensation on a cold water pipe), acidic, or mineral like iron or zinc in contact somewhere with the copper via soil or hardware. Heck if you have ever been in a barn all the copper is green or black from the amonia in the air from urine.
weressl
11-07-2008, 04:31 PM
I agree with you but; DC (AC for that matter) current alone will not turn copper green or black. It takes a chemical or galvanic reaction to turn copper green or black. DC current can accelerate the process, but not cause the reaction. The root cause of the problem is chemical, not current.
My best guess is this is an enviromental condition like moisture (sweating/condensation on a cold water pipe), acidic, or mineral like iron or zinc in contact somewhere with the copper via soil or hardware. Heck if you have ever been in a barn all the copper is green or black from the amonia in the air from urine.
Absolutely as I have pointed out in my other post. Two metals with differences between their ionic characteristics and the presence of an electrolyte as Signore Luigi(not Mario) Galvani discovered it.:smile:
Or to put it another way; one's corrosion is another man's battery.:grin:
Cavie
11-07-2008, 05:21 PM
Have a customer who called because the copper water pipes in his house have turned green. Without getting into all that I found there was current traveling on the copper pipes. I have corrected that condition. Has anyone seen this happen and will the green slowly go away now that the current has been removed? Not sure if the current flow turns copper pipe green.
If it's well water, have it checked for sulfur content. I knew couple that kept the jewelry in the car because it destroyed everything in the house.
LarryFine
11-07-2008, 09:29 PM
Correct but current flow will accelerate the process.As will elevated temperatures.
LarryFine
11-07-2008, 09:37 PM
I know plumbers that have had to re-pipe whole homes from galvanized fittings being used.Does that mean we should use brass/bronze clamps instead of galvanized ones? :confused:
LarryFine
11-07-2008, 09:39 PM
In my case, it was just one hot wire to one of the breakers. The entire end where the insulation was stripped was green except where the screw made contact. It was tight too.I'd be willing to bet that the wire was still being heated despite the tight connection. It still could have been resistive, or the breaker may have been generating heat.
hillbilly1
11-07-2008, 11:09 PM
I have seen where the plumber sweating the fittings, did not wipe the joint after sweating it, cause it to turn green from the left over flux. (which I believe is a corrosive agent)
wptski
11-08-2008, 10:32 AM
I'd be willing to bet that the wire was still being heated despite the tight connection. It still could have been resistive, or the breaker may have been generating heat.
I was looking at a double 30A breaker on a water heater at the time in the PB. This is the only IR image I have that shows enough of that side of the PB where the connection/wires would be. Not the best of images but I've marked where that breaker was and not a single wire is showing up in the image, so there was no heating at all.
http://img.photobucket.com/albums/v373/wptski/WtrHt_Breaker_IR_3.jpg
wptski
11-08-2008, 10:59 AM
I'd be willing to bet that the wire was still being heated despite the tight connection. It still could have been resistive, or the breaker may have been generating heat.
On the other hand this compressor OL that deveoped a high resistance and had a voltage drop or what some refer to as a FOP of 3.2V has a bit of green on it(top of image). So much for the safety of a OL!:rolleyes: The tags are in F not C, not sure why they didn't show in the image.:confused:
http://img.photobucket.com/albums/v373/wptski/SantaFe_1.jpg
http://img.photobucket.com/albums/v373/wptski/SantaFe_IR_1.jpg
LarryFine
11-08-2008, 04:06 PM
. . . I've marked where that breaker was and not a single wire is showing up in the image, so there was no heating at all.Maybe there was no load on at the time of the imaging.
wptski
11-08-2008, 04:35 PM
Maybe there was no load on at the time of the imaging.
True, I really can't say for sure that there was! I'll have to look into it the next time I'm there.
grant
11-18-2008, 07:41 PM
I have been away and finally had time to get back to this post. Thanks for all the info. I am sorry that I gave some bad info. The pipes were not turning geen externally but the water was turning green. When the water was not used during the night the water would turn green and once the water was used in the morning the water would clear up. The water was tested, the owner spend over $12k trying to correct this problem (experts, water filtering system etc.)After we removed the problem with the parallel between the grounded circuit conductor and the copper pipe it appears the water problem has gone away. The water is now clear and the General is getting a bill for the $12K. I don't think the General will be using the Electrical Contractor who did the original install, in the future. Thanks again for all the input.
LarryFine
11-18-2008, 09:40 PM
. . . the General is getting a bill for the $12K.Please let us know how that one goes.
Jason E De Lorenzo Sr
11-18-2008, 10:29 PM
So lightning turner the statue of liberty green?
LarryFine
11-19-2008, 01:51 AM
So lightning turner the statue of liberty green?
No; envy.
George Stolz
11-19-2008, 08:59 AM
After we removed the problem with the parallel between the grounded circuit conductor and the copper pipe it appears the water problem has gone away.
Can you describe what was wrong and what you did in more detail?
Fulthrotl
11-19-2008, 09:12 AM
Can you describe what was wrong and what you did in more detail?
sounds like the local water chemistry has minerals that react with
the copper pipe in the presence of current flow, and overnight the
water stays motionless long enough to be tinted.
grant
11-21-2008, 12:27 AM
Can you describe what was wrong and what you did in more detail?
Home has 400amp service with a 200amp feeder to a sub panel. Original contractor, for what ever reason decided to ground the neutral at the sub panel and bond to the water pipe. We removed the ground and bond. Neutral is bonded at the service panel and connected the the UFER ground which is bonded to the water. As mentioned, by one of the responders to this post, we think the water turned green because it was not flowing during the night and with the current flowing on the pipe caused some type of oxidation or what ever reaction with the copper pipe. Once the water flowed the color would go away until the next night. We are still waiting to hear about the 12K bill to the General.. If I hear gun shots I will let you know.
Thanks again for all the responces.
George Stolz
11-21-2008, 12:33 AM
Original contractor, for what ever reason decided to ground the neutral at the sub panel and bond to the water pipe. We removed the ground and bond.
That's all I was looking for. :cool: