I have a NEMA 4X stainless steel enclosed 800A breaker. The interior is dripping wet due to condensation. The breaker is located "uphill" from the load conduits.

It is a Square D MA1000DS enclosure.

I asked Square D if they have a method to deal with the condensation - "nope".

Other than replacing the enclosure, do you guys have any solutions on how to keep this interior dry??

Buck Parrish
12-01-2008, 11:54 AM
You must have cold and hot air. Which one is the coldest? Is it in the enclosed breaker? If so could you put some duct seal in the conduit(s)

don_resqcapt19
12-01-2008, 02:16 PM
And if sealing the conduits to limit the air exchange doesn't work, you could look at adding an enclosure heater.

ron
12-01-2008, 03:04 PM
Is there duct seal that is tested for use with conductor insulation? Other than that found with E-Y fittings (hazardous locations), I haven't found a good one that has a track record with THWN and THHN, etc.

augie47
12-01-2008, 03:27 PM
http://www.idealindustries.com/products/wire_installation/accessories/duct_seal.jsp

jawbox
12-01-2008, 06:25 PM
Is Gardner Bender Pug Duct seal the same thing??

djcrzysounds@yahoo.com
12-02-2008, 06:34 AM
Get a couple of those silica packs that come with your new boots.... Once you get the moisture out of the enclosure it should be ok.. either that or you have a leak.