12-05-2008, 05:11 PM
we don't use much NM-B, but I know that they are coming out with all types of special cables (12-2-2, etc)....

here is the question, have they come out with a 12/2 romex with 2 grounds? and insulated and a bare in the same outer sheathing?

and would this be legal for the patient care area in a dentists office?

no, i haven't look it up...just thinking...thanks

augie47
12-05-2008, 05:14 PM
no and no
517.13
(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with an effective ground-fault current path by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding conductor in accordance with 250.118.

emahler
12-05-2008, 05:20 PM
thanks...told you it was a silly question...

480sparky
12-05-2008, 05:21 PM
thanks...told you it was a silly question...

Not silly at all. We're all ignorant..... just in different areas.;)

emahler
12-05-2008, 05:29 PM
Not silly at all. We're all ignorant..... just in different areas.;)

i bet you i got you beat:D

360Youth
12-05-2008, 05:51 PM
thanks...told you it was a silly question...

I have been on a CS Lewis kick lately, so here you go...

"Can a mortal ask questions which God finds unanswerable? Quite easily, I should think. All nonsense questions are unanswerable. "


All kidding aside, it is amazing how many different products I have learned of since perusing around here, so it is never a silly question to ask of such things.

infinity
12-05-2008, 06:53 PM
A 12-2 with two grounds could be used for isolated ground circuits.

nolabama
12-05-2008, 07:10 PM
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?

mxslick
12-05-2008, 08:52 PM
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?

I think the 12-2-2 is actually 2 hots, two neutrals and a bare ground. :D

Brought about because of those PITA AFCI's.

emahler
12-05-2008, 09:32 PM
A 12-2 with two grounds could be used for isolated ground circuits.

with a plastic box, 12-2 with 1 ground could be used for an IG circuit

480sparky
12-05-2008, 09:34 PM
A 12-2 with two grounds could be used for isolated ground circuits.


How would you keep them (being bare and all) from each other when you screw the recep into the box?

emahler
12-05-2008, 09:36 PM
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?

not for an inspector:D

Fulthrotl
12-05-2008, 09:49 PM
I have been on a CS Lewis kick lately, so here you go...

"Can a mortal ask questions which God finds unanswerable?


actually, no.

can God's answer to an unanswerable question be in a form
that a mortal is unwilling to accept?

here we go.........:D
this is meaner than smearing peanut butter on the roof of
a dogs mouth.

randy

360Youth
12-05-2008, 10:14 PM
this is meaner than smearing peanut butter on the roof of
a dogs mouth.

randy

It's been years since I've done that. Ahhhh, the memories. :D

480sparky
12-05-2008, 10:40 PM
i bet you i got you beat:D

I'll concede that one.... I guarantee I'm more ignorant than you!:smile:

nolabama
12-05-2008, 10:42 PM
the only thing we use 12-2-2 for here is heater/vent/light switch legs - what do you mean that this came about for AFCI's ?

Pierre C Belarge
12-05-2008, 10:43 PM
dumber question wouldnt 12-2 with an inuslated and bare ground be 12-3 with one of the wires green instead of red - and if so wouldnt a roll of green tape fix that ?


take a peek at 250.119.

480sparky
12-05-2008, 10:44 PM
the only thing we use 12-2-2 for here is heater/vent/light switch legs - what do you mean that this came about for AFCI's ?

You can't use 12/3 or 14/3 for two AFCId circuits. So 14-2-2 and 12-2-2 were developed.

nolabama
12-05-2008, 10:46 PM
"take a peek at 250.119"
the continuous part messes that up:D

nolabama
12-05-2008, 10:50 PM
You can't use 12/3 or 14/3 for two AFCId circuits. So 14-2-2 and 12-2-2 were developed.

i guess i dont follow - AFCI's are mostly only put in for inspection 'round here and promply pulled out - so you guys pull two homerun circuts on a 12-2-2 (its even refered to as 12/4 here) and j-box when you get where your going??

ctmike
12-05-2008, 10:53 PM
i guess i dont follow - AFCI's are mostly only put in for inspection 'round here and promply pulled out - so you guys pull two homerun circuts on a 12-2-2 (its even refered to as 12/4 here) and j-box when you get where your going??

dont confuse 12-2-2 with 12-4 12-2-2 has two grounded conductors where 12-4 is red white black and blue I belive

nolabama
12-05-2008, 10:58 PM
dont confuse 12-2-2 with 12-4 12-2-2 has two grounded conductors where 12-4 is red white black and blue I belive

thanks that is clearly what i have been doing - the 12-2-2 is black, red, white, candy stripe white, and bare - 12-4 would be black, red, blue, and white - i thought they were the same thing :-?

LarryFine
12-06-2008, 01:24 AM
517.13
(A) Wiring Methods. All branch circuits serving patient care areas shall be provided with an effective ground-fault current path by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding conductor in accordance with 250.118.So, just have the NM sheath copper-plated. 8-)

Mr.Sparkle
12-06-2008, 01:50 AM
AFCI's are mostly only put in for inspection 'round here and promply pulled out

I am not sure I follow that logic :-?, aside from the liability thing wouldn't the task of doing so not quite outweigh the savings in the end?

emahler
12-06-2008, 09:30 AM
I'll concede that one.... I guarantee I'm more ignorant than you!:smile:

guarantee you aren't