View Full Version : service grounding


wireperson
12-06-2008, 01:34 AM
does it need to be a bare conductor or it can be insulated , prints call for a #2 thwn , its a 400 A service

Rockyd
12-06-2008, 01:46 AM
250.119 and 250.119(A)

Bare is probably cheaper, but if six or larger, re-identify.

infinity
12-06-2008, 04:19 AM
What size are the service entrance conductors? #2 sounds small. It could be bare or insulated and is not required to be green.

http://www.mikeholt.com/onlinetraining/page_images/1113920706_2.jpg