I have a 20,000sq/ft building where all the lighting is compact fluorescent. I leave the panel with A,B,C and one neutral. During a neutral fault test, I find continuity between the neutral and EGC. So we pull the neutrals off the buss and show no current on the EGC as we energize each circuit one by one.
So I get a new uninstalled fixture and test, no continuity, lamp it and still no continuity.
How could this happen?
buddhakii
02-02-2009, 09:51 PM
Did you read continuity with the neutral disconnected from the buss? If so I would say you have a couple neutrals of different circuits tied together. With the neutral disconnected did the lights still come on? If this is a mwbc I wouldn't turn circuits on with the neutral disconnected as you can do a lot of damage.
Dead short continuity or high resistence continuity?? I've seen some wierd things with flour.ixtures before.
benaround
02-03-2009, 01:58 AM
Reading thru the wye connected transformer ? Really need to know exactly how you did
the test.
Did you read continuity with the neutral disconnected from the buss? If so I would say you have a couple neutrals of different circuits tied together. With the neutral disconnected did the lights still come on? If this is a mwbc I wouldn't turn circuits on with the neutral disconnected as you can do a lot of damage.
Bingo!.......
iwire
02-03-2009, 03:58 PM
If this is a mwbc I wouldn't turn circuits on with the neutral disconnected as you can do a lot of damage.
Chris is well aware of basic wiring procedures. :smile:
mxslick
02-03-2009, 04:29 PM
So we pull the neutrals off the buss and show no current on the EGC as we energize each circuit one by one.
Bob, I too was about to chime in on energizing MWBC with lifted neutrals until I re-read a few times and noticed the phrase in bold. :D
chris kennedy
02-03-2009, 05:41 PM
I don't know if this would make a difference but the battery in the DMM I used died today. Tomorrow I will be back in the panel and will also test with a Fluke T+ and the DMM. BTW, the DMM is an Ideal 61-774. I'll let you know.
buddhakii
02-03-2009, 06:26 PM
Chris is well aware of basic wiring procedures. :smile:
I would've thought so, but no matter how familiar someone is with anything doesn't mean we forget things. I missed the one by one part too.
chris kennedy
02-03-2009, 06:30 PM
I would've thought so, but no matter how familiar someone is with anything doesn't mean we forget things. I missed the one by one part too.
I agree and it doesn't hurt to state the obvious. Keep them coming.
cowboyjwc
02-03-2009, 07:32 PM
If you are simply trying to see if the neutral is clear, don't use a real sensitive meter. We were doing the same test once and found out it was reading between our fingers. I would just use one of the cheap,flashlight types.
Also anytime we do one of these tests and someone blames the transformer or lights it still usually ends up being a pinched wire or something silly like that.
benaround
02-03-2009, 07:40 PM
No new Exit or EMG fixtures on these circuits ? Occupancy sensors ?
Your test was in the circuit downstream of the panel, is that right? From load side neutral
to EGC.
No new Exit or EMG fixtures on these circuits ? Occupancy sensors ?
Your test was in the circuit downstream of the panel, is that right? From load side neutral
to EGC.
The user doesn't have something like an old 3 wire dryer or range that connects one hot leg to ground/neutral to derive 120V for a timer or lamp does it?
chris kennedy
02-04-2009, 05:49 AM
If you are simply trying to see if the neutral is clear, don't use a real sensitive meter.
Trying this morning with different meters.
Also anytime we do one of these tests and someone blames the transformer or lights it still usually ends up being a pinched wire or something silly like that.If this was the case, then with the grounded conductor lifted from the buss and the circuits energized one and only one at a time, I would have had current on the EGC and the lights would operate.
No new Exit or EMG fixtures on these circuits ? Occupancy sensors ?
Your test was in the circuit downstream of the panel, is that right? From load side neutral
to EGC.
Correct, and of the 40 or so lighting circuits, only 3 or 4 have no new LED type exit/emergency lights on them.
The user doesn't have something like an old 3 wire dryer or range that connects one hot leg to ground/neutral to derive 120V for a timer or lamp does it?
No, brand new building.
mxslick
02-04-2009, 04:23 PM
Based on all the info and answers so far, the only thing I can think of is this:
The leakage resistance from neutral to ECG in EACH fixture is of a very high value, but put enough of them together on any given circuit and the resistance drops enough to be readable.
The ultimate question I have is this: if AFCI's aren't involved, and the circuits function properly, why the fuss?
Another approach to take:
With the neutrals properly attached to the bus, power up the fixtures and lift the EGC's and see if there is appreciable voltage built up with a wiggy in parallel with a DMM, or leave the EGC's attached and see if there is current flow.
cowboyjwc
02-04-2009, 06:18 PM
The ultimate question I have is this: if AFCI's aren't involved, and the circuits function properly, why the fuss?
If it's a system that requires a GFCI, you want to make sure that it's clear so that you don't get any nuciance tripping. That is actually one of the test's they do when they test the GFCI and will usually note if all of the circuits are not connected when they do the test.
Now of course I'm assuming that the lighting is 277 and that the service is rated at 1000 amps or more.
chris kennedy
02-04-2009, 06:31 PM
If it's a system that requires a GFCI, you want to make sure that it's clear so that you don't get any nuciance tripping. That is actually one of the test's they do when they test the GFCI and will usually note if all of the circuits are not connected when they do the test.
Now of course I'm assuming that the lighting is 277 and that the service is rated at 1000 amps or more.
800A 208Y/120. But I'm in the habit of doing this test due to the number of GFI protected services we have done in recent years. Unfortunately it was a circus today and I didn't have a chance to get back into the panel. Poco power comes tomorrow, so I doubt I can test until Friday.
cowboyjwc
02-04-2009, 07:01 PM
800A 208Y/120. But I'm in the habit of doing this test due to the number of GFI protected services we have done in recent years. Unfortunately it was a circus today and I didn't have a chance to get back into the panel. Poco power comes tomorrow, so I doubt I can test until Friday.
Not a bad habit to get into and it's not like it's hard to do. I usually just have them pull the neutral disconnect link and check there.
chris kennedy
02-04-2009, 07:20 PM
Not a bad habit to get into and it's not like it's hard to do. I usually just have them pull the neutral disconnect link and check there.
From an inspectors point of view.:smile: For the installer, it's much quicker to go to each panel and while the panels are not energized, take all the grounded conductors off the buss, check each one for continuity to ground. Quickly identifies the circuits in question. Thats how I found this (http://i203.photobucket.com/albums/aa80/chris_kennedy/bullseye002.jpg) on the same job.
With multiple panels, simply removing the bonding jumper may tell you you have a problem, but where to look? It's like pulling wire, work your way from the furthest point to the source.
cowboyjwc
02-04-2009, 07:48 PM
You are correct, my way will tell you, you have a problem, you can then pull the grounded conductors and isolate which panel and then you are still going to have to do it your way to isolate the circuit.
chris kennedy
02-04-2009, 08:00 PM
you can then pull the grounded conductors and isolate which panel
Again, from the installers point of view, I'm not going to pull 4,6,8 large neutrals that have already been torqued out of MDP to find a problem. I will pull 20 small conductors out of 4 to 8 panels quicker. Work from the outside in.
benaround
02-04-2009, 08:23 PM
I'll bet you have continuity through the exit or emg fixtures.
chris kennedy
02-04-2009, 08:32 PM
I'll bet you have continuity through the exit or emg fixtures.
I got that from your earlier post. Ran out of time today but will be checking with multiple meters and will let you know.
winnie
02-04-2009, 10:57 PM
I leave the panel with A,B,C and one neutral. During a neutral fault test, I find continuity between the neutral and EGC. So we pull the neutrals off the buss
Could you describe the method and meter you used for the test?
I would assume that you lift the neutral and then check for continuity between neutral and ground, however you describe doing the test and _then_ pulling the neutrals off the bus.
-Jon
Chris, when you pulled the grounded conductors off the neutral bar in the sub-panels did the lights try to come on come on as you energized each branch circuit ONE by ONE.
I've used this method successfully to find ground wires touching neutrals.
cadpoint
02-05-2009, 12:59 AM
Could you describe the method and meter you used for the test?
I would assume that you lift the neutral and then check for continuity between neutral and ground, however you describe doing the test and _then_ pulling the neutrals off the bus.
-Jon
:) yeah what he said! :) Only cause I put it to the search engine test...
Frankly, I first thought the color blind electrician, got in there! But my second thought was how could you be finding this with dead batteries ?
Where's the half way rule, go half way down a circuit and then back of equal distance again depending on the reading.
I kinda like the thought about a summary from the loads but ruled that out because its a lighting load. Gezz maybe I'll have to check and lift myself!
Check the batteries in the fluke 1507, and you won't have to do 2X the lifting!
chris kennedy
02-05-2009, 05:17 AM
Could you describe the method and meter you used for the test?
From the top:
1) Open all branch circuit breakers in the panel
2) Pull all branch circuit grounded conductors off the buss
3) Test branch circuit grounded conductors for continuity to EGC
4) Lets say suspect neutral is labeled 2,4,6. Cap neutral and turn on 2. Check for current on the branch circuit EGC. None found, lights still off. Turn 2 off and 4 on, same results, repeat for 6.
5) Scratch head, post very confusing thread.
Meter used was an Ideal DMM 61-774, battery suspect.
winnie
02-05-2009, 10:55 AM
Chris,
At step 3, did you touch the probes to the wire, get the continuity beep, and release? Or did you hold the probes in place for a period of time and have the continuity beep for the entire time?
When you measured a single uninstalled fixture, did you set the meter to its various resistance ranges and get a resistance value between fixture neutral and ground?
-Jon
Chris, I too have an Ideal DMM and if the battery is getting weak all bets are off, it really goes crazy.
Also, remember there are multiple paths for fault current to return to a panel other than the bare wire. All the building steel is an EGC, per Code.
You really should switch to a megger, a nine volt test won't find leakage current in a mile of wire and you need to assign numbers to your findings.
I admire your tenacity, some would call it a wrap, since everything works...for now.
chris kennedy
02-05-2009, 06:54 PM
Chris, I too have an Ideal DMM and if the battery is getting weak all bets are off, it really goes crazy.
Today went back in with new batteries in the Ideal and Greenlee CM-850, which is my DMM of choice, but the battery was weak in that when we started the first test. Also used the Fluke T+. No neutral faults where found.
At step 3, did you touch the probes to the wire, get the continuity beep, and release? Or did you hold the probes in place for a period of time and have the continuity beep for the entire time?
This was a mistake on my part Jon. I don't just flash the probe to the conductor, I hold it there. The Ideal was kind of spurting and sputtering with the beeps, but with a meter not often used, I was just thinking poor contact due to dirty leads.
I thank you all and hope I didn't waste too much of any ones time. I will try to be more thorough before I get my friends chasing my ghosts. At least I learned something from this.
Today went back in with new batteries in the Ideal and Greenlee CM-850, which is my DMM of choice, but the battery was weak in that when we started the first test. Also used the Fluke T+. No neutral faults where found.
This was a mistake on my part Jon. I don't just flash the probe to the conductor, I hold it there. The Ideal was kind of spurting and sputtering with the beeps, but with a meter not often used, I was just thinking poor contact due to dirty leads.
I thank you all and hope I didn't waste too much of any ones time. I will try to be more thorough before I get my friends chasing my ghosts. At least I learned something from this.
Great Chris, glad you found it, we all learn from these exercises.
chris kennedy
02-05-2009, 07:33 PM
Great Chris, glad you found it, we all learn from these exercises.
You won a weeks stay in one of the guest room here. Please book that while I'm away, there is only one computer.:D