View Full Version : Number of Load Side Receptacles
A-1Sparky
02-05-2009, 03:31 PM
Is there a code-mandated maximum number of receptacles that can be protected off the load side of a GFI? What about manufacturer recommended limits?
billsnuff
02-05-2009, 03:47 PM
follow manufacturers recommendations IMHO, no NEC limit in resi, 180VA commercial, i think....
raider1
02-05-2009, 04:07 PM
There is no NEC maximum number of receptacles that are premitted to be installed downstream from a GFCI receptacle. You would need to follow the manufactures installation instructions (110.3(B)).
Chris
A-1Sparky
02-05-2009, 04:14 PM
Thanks guys.
raider1
02-05-2009, 04:19 PM
Your very welcome.:)
Chris
vBulletin® v3.7.3, Copyright ©2000-2009, Jelsoft Enterprises Ltd.