03-04-2009, 05:39 AM
I would usually go underground for this....never have done it overhead. Doing a 200A meter combo upgrade. Relocating meter from house to detached garage and GC wants to do 100A subfeed back to house as an overhead feed. Its about 30-40 ft through backyard to subpanel location. Do I go w/ #4 THHN or should I get some kind of triplx for this. At 40' will I need a pole between to maintain clearance??
active1
03-04-2009, 06:57 AM
The first thing that comes to my mind is 310.15(B)(6)
For dwelling units, conductors as listed in 310.15(B)(6), shall be permited as 120/240-volt , 3-wire, single phase service-entrances conductors, service lateral conductors, and feeder conductors THAT SERVE AS THE MAIN POWER FEEDER TO A DWELLING UNIT and are in a raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder(s) between the main disconect and the lighting and appliance branch circuit panelboard.
I see too many times #4 THWN run for 100a or #2/0 TWWN run for 200a 3 phase pannels in my area.
With a 100a feerder you would meet the requirements of 225.6(A)(1) - #8 copper or #6AL unless supported by a messenger wire. Myself I would still use a messenger wire.
Quote:
At 40' will I need a pole between to maintain clearance??
That would depend on the drop heights and what your spanning. I would guess at least 1 side needs to be higher than 1 story.
Depending on your grounding situation you would need triplex or quadplex. Myself I like to uses an equipment grounding conductor even if there is no other metalic paths between structures. Reason is it's still safe if they create a metalic path later.
Based off 2002 NEC as I don't have the other versions with me.
Dennis Alwon
03-04-2009, 08:10 AM
I would usually go underground for this....never have done it overhead. Doing a 200A meter combo upgrade. Relocating meter from house to detached garage and GC wants to do 100A subfeed back to house as an overhead feed. Its about 30-40 ft through backyard to subpanel location. Do I go w/ #4 THHN or should I get some kind of triplx for this. At 40' will I need a pole between to maintain clearance??
I don't believe T.310.15(B)(6) can be used in this situation since it does not carry the entire load of the service. You need to use T. 310.16
No you cannot use #4 nor can you use THHN. You must use a 4 conductor cable that is suitable for this install if you are under the 2008 code. I would read art. 250.32(B) of whatever code you are using.
tryinghard
03-04-2009, 10:05 AM
I would usually go underground for this....never have done it overhead. Doing a 200A meter combo upgrade. Relocating meter from house to detached garage and GC wants to do 100A subfeed back to house as an overhead feed. Its about 30-40 ft through backyard to subpanel location. Do I go w/ #4 THHN or should I get some kind of triplx for this. At 40' will I need a pole between to maintain clearance??
Make sure your 100A feeder is correctly sized for the calculated load of the house. THHN is not sunlight compatible, you’ll need quad-plex aerial and it’s usually aluminum for weight, the neutral cannot common with the equipment grounding on your sub feed this would be a violation(250.24(5) & 250.142(B)). The span distance is up to you but a compliant overhead feed I believe must be 10’+ above grade (you should verify this with NEC; see 225.18), I don’t think your span needs a pole if you obtain the height as long as your risers are compatible.
I don't believe T.310.15(B)(6) can be used in this situation since it does not carry the entire load of the service. You need to use T. 310.16
Dennis, that article specifically mentions feeders too.
augie47
03-04-2009, 10:24 AM
My comments:
a. IMHO, 310.16 for your conductors {310.15(B0(6) is at best debatable}
b. conductors must be sunlight resistant
c. in this area AL ACSR is normally used due to messanger..(if ASCSR is used those conductords must terminate outside at the drop)
d. Address 250.32 depending on your Code Cycle and other varibles (in 2008 you must have a EGC)
e. Address 250.32 as far as your gounding electrodes at the residence.
active1
03-04-2009, 09:39 PM
Dennis, that article specifically mentions feeders too.
310.15(B)(6)
...... and feeder conductors THAT SERVE AS THE MAIN POWER FEEDER TO A DWELLING UNIT..... For application of this section, the main power feeder(s) between the main disconect and the lighting and appliance branch circuit panelboard.
Being the feeder is going to a detached garage and not a dwelling unit 310.15(B)(6) would not apply IMO.
I would guess that the intent of the feeder statement in that section is for when you have a situation such as a disconect on the meter or 1 disconect for a multi family meter bank.
Dennis Alwon
03-04-2009, 09:45 PM
Dennis, that article specifically mentions feeders too.
Yes it does but as I mentioned it must carry the entire load of the service. If the service is 200 amps and you are running a 100 amp feeder to the house then that feeder does not qualify to use 310.15(B)(6), IMO. It probably should but the way the code is written I say no go.
JohnJ0906
03-05-2009, 08:14 AM
Yes it does but as I mentioned it must carry the entire load of the service. If the service is 200 amps and you are running a 100 amp feeder to the house then that feeder does not qualify to use 310.15(B)(6), IMO. It probably should but the way the code is written I say no go.
"....and feeder conductors that serve as the main power feeder to each dwelling unit....."
No mention of entire service load.
GC wants to do 100A subfeed back to house as an overhead feed. 310.15(B)(6) applys, as long as that 100 amp feeder carries the entire house load.
Dennis Alwon
03-05-2009, 08:25 AM
"....and feeder conductors that serve as the main power feeder to each dwelling unit....."
No mention of entire service load.
310.15(B)(6) applys, as long as that 100 amp feeder carries the entire house load.
I sit corrected. :D
Dennis Alwon
03-05-2009, 03:18 PM
I sit corrected. :D
I gave up too easily. :smile:
"....and feeder conductors that serve as the main power feeder to each dwelling unit....."
No mention of entire service load.
Art. 310.15(B)(6) states this:
... For application of this section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling unit.
Would you not consider the garage whether remote or not to be associated with the dwelling unit? I would thus I will recant and state that T. 310.15(B)(6) is not applicable.
augie47
03-05-2009, 03:55 PM
I gave up too easily. :smile:
Art. 310.15(B)(6) states this:
Would you not consider the garage whether remote or not to be associated with the dwelling unit? I would thus I will recant and state that T. 310.15(B)(6) is not applicable.
In my post (#6) I stated "debatable", but, personally I agree with you.
The garage is "associated" and 310.15(B)(6) is not applicable.
I gave up too easily. :smile:
Art. 310.15(B)(6) states this:
... For application of this section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling unit.
Would you not consider the garage whether remote or not to be associated with the dwelling unit? I would thus I will recant and state that T. 310.15(B)(6) is not applicable.
It is the main feeder between the main disconnect and the panelboard and that dwelling panelboard does contain all the branch circuits, feeders, etc that serve that dwelling unit.
I might be all wrong on this but, doesn't table 310.20 apply to the portion of conductor that is in free air then after the splices to the others conductors( in the conduits or cables) then 310.16 would apply.
as far as the 40 ft. span, I don't see a need for a lift pole as long a the anchoring points on the strucure a properly installed.
augie47
03-05-2009, 08:10 PM
good call pjg, I forgot the "free air".