06-26-2009, 12:02 AM
Have you ever installed SD inside bathrooms?
tonyou812
06-26-2009, 12:28 AM
I cant ever recall ever having to. Nor do I ever recall seeing any. Maybe on an airplane or school. Hey your from my neck of the woods. Are you keeping busy?
mtnelectrical
06-26-2009, 01:00 AM
not really, last couple months very slow, but I have like 3 aditions waiitng for approval, let's see what happens. Qre you in Essex too?
quogueelectric
06-26-2009, 01:17 AM
not really, last couple months very slow, but I have like 3 aditions waiitng for approval, let's see what happens. Qre you in Essex too?
Always strobes but there was always drama over proper location where strobe can be seen from in the bathroom.
resistance
06-26-2009, 02:29 AM
Sounds like a building code question to me. Do they call them smoke detectors in a commercial environment?
tonyou812
06-26-2009, 10:26 AM
not really, last couple months very slow, but I have like 3 aditions waiitng for approval, let's see what happens. Qre you in Essex too?
Yes sir. Montclair, Verona, Cedar Grove, The Oranges, Maplewood areas.. and of course Newark ....:smile:
ultramegabob
06-26-2009, 12:31 PM
I have never installed a smoke detector in a commercial building, they are only required in residential around here...
MNWildcat
06-26-2009, 05:43 PM
Yes.
Smoke detectors may be required in a bathroom, for that matter, one could be required anywhere/everywhere.
For example in a hospital for smoke damper control, the damper can be controled by a dedicated duct detector (which are prone to false alarms) or total area detection can be used to close the damper. The total area detection requires a smoke detector in every room fed by the HVAC system, including restroom/toilets.
Though NFPA 72 does state that smoke detectors shall not be installed in areas that are too extreme, so where there are showers the somke detectors may not want to be used due to false alarms (steam looks like smoke to the detector).
LarryFine
06-26-2009, 07:17 PM
I have not.
Yes sir. Montclair, Verona, Cedar Grove, The Oranges, Maplewood areas.. and of course Newark ....:smile:Name-dropper! (:grin:)
mtnelectrical
06-30-2009, 06:13 PM
Tonyou812. So you are the low bidder that is taking all the jobs? lol...
iMuse97
07-01-2009, 03:43 AM
Yes.
Smoke detectors may be required in a bathroom, for that matter, one could be required anywhere/everywhere.
For example in a hospital for smoke damper control, the damper can be controled by a dedicated duct detector (which are prone to false alarms) or total area detection can be used to close the damper. The total area detection requires a smoke detector in every room fed by the HVAC system, including restroom/toilets.
Though NFPA 72 does state that smoke detectors shall not be installed in areas that are too extreme, so where there are showers the somke detectors may not want to be used due to false alarms (steam looks like smoke to the detector).
couldn't you install the ionization-type detector in this case?
MNWildcat
07-01-2009, 12:54 PM
couldn't you install the ionization-type detector in this case?
Ion smokes are still sensitive to high humidity and are not as good as photo types oveall. Also, I would not mix types as having a few ions in some rooms and photos in the rest of the facility. It would be hard for the facility guys to know which is which when they need cleaning/replacement.
Also, there is such a small percentage of the air flow going to a small toilet/shower room relative to the rest of the HVAC zone that other detectors will sense the smoke first anyway.