PetrosA
07-08-2009, 09:40 PM
I was at a customer's house today and ran a line to the panel. Any time I open a panel, I check the connections at the main, and check the screw terminals on all the breakers just for safety. Well, one leg feeding the main was warm to the touch. IR reading showed 30°C on that leg and 24°C on the other with an ambient temp of 24°C. No AC on, so something had to be wrong in the main. In addition the handle was broken off, so if it had tripped the customer wouldn't be able to reset it. It was an old Crouse-Hinds 200A. My SH happened to have one on the shelf so I talked the lady into changing the breaker.
Once I got home I tore the old one apart. Looks like the loose lug caused light arcing and pitted the lug interior somewhat (there's a lug body that slips over a plate which feeds the breaker mechanism and the pitting was in the contact area between the plate and lug body) . If the handle had been ok, I think I probably could have just tightened the lugs and been done with it. What do you think of a quick fix like that on a (possibly) 35-40 year old breaker?
Once I got home I tore the old one apart. Looks like the loose lug caused light arcing and pitted the lug interior somewhat (there's a lug body that slips over a plate which feeds the breaker mechanism and the pitting was in the contact area between the plate and lug body) . If the handle had been ok, I think I probably could have just tightened the lugs and been done with it. What do you think of a quick fix like that on a (possibly) 35-40 year old breaker?