09-29-2009, 08:04 AM
Good morning,

Working for a friend, they built a pole barn on some hunting property and have a meter socket 300 foot away at the road. Building inspector not the electrical inspector stated to run two 4/0 USE-2 aluminum wires and one ground from the socket to the barn and it will pass. the panel in the barn is a 200amp panel. I stated they can cost effectively use 2/0 USE-2 Aluminum but would need 3-2/0 cables and a ground (2-hots 1-neutral and ground). Who's right and if I'm wrong please tell me why. Keep in mind the building inspector is making this statement not the electrical inspector.

LHarrington

1793
09-29-2009, 08:16 AM
Good morning,

Working for a friend, they built a pole barn on some hunting property and have a meter socket 300 foot away at the road. Building inspector not the electrical inspector stated to run two 4/0 USE-2 aluminum wires and one ground from the socket to the barn and it will pass. the panel in the barn is a 200amp panel. I stated they can cost effectively use 2/0 USE-2 Aluminum but would need 3-2/0 cables and a ground (2-hots 1-neutral and ground). Who's right and if I'm wrong please tell me why. Keep in mind the building inspector is making this statement not the electrical inspector.

LHarrington

Look at Table 310.16 for wire sizes. What is the connected load going to be?

LHarrington
09-29-2009, 08:32 AM
thank you for replying they are looking at a few outlets, outside light, heater and indoor lights, Misc. shop tools. My main question was who's right on the amount of conductors?

LHarrington

LHarrington
09-29-2009, 08:35 AM
Sorry just reread you post, they claim less than 100amps but they are using a 200amp panel because they already have it and their thought process was size it large for the future.

LHarrington

1793
09-29-2009, 08:38 AM
thank you for replying they are looking at a few outlets, outside light, heater and indoor lights, Misc. shop tools. My main question was who's right on the amount of conductors?

LHarrington

Where is the first OCPD, at the Meter or Panel in Pole Barn?

LHarrington
09-29-2009, 08:59 AM
haven't seen it myself but he stated it at the meter.

LHarrington

iMuse97
09-29-2009, 09:09 AM
If he has an OCPD at the meter, you would be correct in requiring the EGC back to that point, where it will be bonded to the neutral and the Grounding Electrode Conductor.

cadpoint
09-29-2009, 09:15 AM
It's time to talk to the client and have them identify all their reqirements, you might also ask them to rethink it again for all that future usuage.

If you know the area and know what others put in thier pole barn, well you could suggest things, You get the idea...

You can put a 100 amp breaker on a larger panel. You can even put the bigger wire in and be ready for later.

You will need to calculate all the loads of all the "equipment" that will be put in place. Additional Calc. Non-Dwelling (Code), something like that. You can assume (and show the math) of the future things to also show your client.
Then as long as they are not putting in a later silo or turn it into something unrelated, I think you'll be fine.

While your not required to show the future calculation, its just something to make the client totally grasp everything, and shows you on your game.

jxofaltrds
09-29-2009, 09:26 AM
Depends on what code cycle are you using?

You could do as the inspector says.

LHarrington
09-29-2009, 10:15 AM
I had referred to both 2002 and 2005 NEC, That's where I'm stuck I didn't want to tell the building Inspector he was wrong, just making sure it's right or correctly done.

LHarrington

iMuse97
09-29-2009, 10:46 AM
Not thinking far enough, but only thinking as to what I would do... I stand corrected: you could do as suggested by the building inspector, depending on code cycle, for example.

mcclary's electrical
09-29-2009, 11:23 AM
Not thinking far enough, but only thinking as to what I would do... I stand corrected: you could do as suggested by the building inspector, depending on code cycle, for example.

I agree, this would pass under 2005, as long as no other metallic paths. But is no longer legal under 2008. I did one last year in the same fashion.

LarryFine
09-29-2009, 01:02 PM
LH, I'd stick with the larger line conductors merely for the distance of the run. You don't want to have to do this job again.

The neutral needs to be sized for the greatest possible 120v load on either line, and no smaller than the allowable EGC.

If you're not yet bound by the 2008 NEC, three conductors are permissible, even though you're past the main disconnect.