horsegoer
10-02-2009, 07:06 AM
I am an estimator and really need some help with this area such as the control, monitoring/status, purge dampers, how fire alarm ties in. Does anyone know of good literature/courses or someone can give me an overview. Thanks very much.

horsegoer
10-02-2009, 10:21 PM
Anyone????

stevenj76
10-02-2009, 10:36 PM
Smoke dampers will with 120V by the electricians, from your box.

nhfire77
10-03-2009, 03:53 PM
I would think that the FACP would have a addressable module to trip the activation.

You the dampers may have limit switches that monitor position. Those could be tied into supervisory modules.

The dampers I have seen installed were 24 VDC and had to have a back up power supply. Of course then that has to have an relay and a monitoring module of its own.

Personally I would want to see the manufacturers specs before costing it out.

cadpoint
10-03-2009, 07:30 PM
NFPA-72 (http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=72http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=72), this is the book right here! I believe you have the accounting part down.
http://www.nfpa.org/catalog/images/products/7210_sm.jpg
2010, right off the press!
But as earlier said, you'll have to account for all the various devices and the linear runs and how each is wired, series Vs parallel, zones, etc.

Once you get over the paradox of DC being involved, I think you'll be fine... :grin:

benaround
10-04-2009, 09:31 PM
I would think that all the info that you need is right in the prints, Electrical, Mechanical, &

FA. Mech. supply and install, Elec. to supply what ever power, FA to tie it into the FACP.

quogueelectric
10-04-2009, 10:36 PM
Anyone???? Give me a call you knucklenose I will totally hook you up.

Stallzer
10-06-2009, 08:52 PM
It's a pretty loaded question.
Things that apply

1. Building classification
2. Fire / Smoke damper or Fire Damper
3. Complete Smoke Detector Coverage ? See #1

Each Building classification comes with unique Fire and Life Safety guidelines as well as your local Authority having jurisdiction.

RJohnsonMasterElectrician
10-27-2009, 08:55 PM
when I wire a FSD I use a R10E with a FRM. If I can get the time I will post the wiring diagram.

TLBryant
11-24-2009, 10:38 AM
Should be on drawings or in specs. This is typical of what I see:

Smoke damper installed by HVAC with a 120VAC power source.

Smoke detectors or duct smoke detectors activate a relay or an addressable relay module that tells the damper to close. Duct detectors will also shut down the air handler.

Some dampers have a limit switch to allow monitoring of damper open/close. This could wired to a non-alarm zone or connected to an addressable monitor module(s).

drawfire
12-08-2009, 03:57 PM
Link for Fire/Life Safety Product Training - Dampers. (No affiliation just good basics from the web). http://jacksonsystems.com/themes/jackson//pdf/firetraining.pdf

Code References
NFPA 70, 72, 90A
IBC 716, 907
IMC 606, 607
UL 1971