laketime
10-02-2009, 09:29 PM
I am installing a 1" pvc underground run from a generator to a house. The run will be about 300'. I want to put a pull point in the run, would you guys suggest a hand hole type box or a weather proof box mounted above the ground. The area it will be in had 7' of snow last year
Buck Parrish
10-02-2009, 09:34 PM
If you have to make a splice. Above ground would be a better option.
Johnmcca
10-02-2009, 09:34 PM
I'd go with the hand hole, unless you want to put it on a pole, to put it above the snow pack.
Do you expect problems with your installation?:)
mcclary's electrical
10-02-2009, 09:34 PM
I am installing a 1" pvc underground run from a generator to a house. The run will be about 300'. I want to put a pull point in the run, would you guys suggest a hand hole type box or a weather proof box mounted above the ground. The area it will be in had 7' of snow last year
Is it straight?,,,,,
what's going in it? ,,,Most likely, I would just pull it without one
I'd go no pull points and steel 90's.8-)
hardworkingstiff
10-02-2009, 09:38 PM
I'd go no pull points and steel 90's.8-)
I 2nd this recommedation assuming you don't go over the 360-degrees of bending.
Power Tech
10-02-2009, 09:57 PM
I will 3rd or 4th that. No pull box / No J-box.
Steel 90 on the pull end like the PP.
Any bends make them gradual.
Every bend is a brake shoe.
Buck Parrish
10-03-2009, 12:06 AM
Better yet direct burial cable, no conduit.
iMuse97
10-03-2009, 12:15 AM
I'd do direct burial if possible.
But your suggested size of run (1") and the gennie feed leads me to ask what size wire and what size gennie you would be installing, and for what load?
Better yet direct burial cable, no conduit.
You think direct burial cable is better than wire installed in conduit?:confused:
Buck Parrish
10-03-2009, 12:44 AM
You think direct burial cable is better than wire installed in conduit?:confused:
Yes, for certain applications.
It's what powers my house. And millions more.
LarryFine
10-03-2009, 01:00 AM
You think direct burial cable is better than wire installed in conduit?:confused:Depends on who's paying for it. ;)
Pierre C Belarge
10-03-2009, 01:44 PM
I would also suggest no pull point, if the run is fairly straight. But I do not know what the elevation change is, the size of the conductors and other parameters that help to determine if a pull point is necessary.
I live in an area where we get rain and snow during the year. Generally the contractors here are using the handhole enclosures more and more. They offer a lot of flexibility. When installed properly, rain and snow are not much of an issue.
laketime
10-03-2009, 02:00 PM
I will be pulling (7) #8's and (4) #12's in it. It is an 8kw generator.
growler
10-03-2009, 02:48 PM
I am installing a 1" pvc underground run from a generator to a house. The run will be about 300'.
I will be pulling (7) #8's and (4) #12's in it. It is an 8kw generator.
See you are already screwing yourself. You don't need a pull box in the middle of the run you need bigger conduit. Run 1 1/4" PVC and see if that doesn't pull just a bunch easier.
Sure the 1 1/4" will cost a little more but in the end you can never go wrong by making the pull as easy as possible.
iMuse97
10-03-2009, 03:38 PM
I will be pulling (7) #8's and (4) #12's in it. It is an 8kw generator.
what the sleeping dog said... and why I asked the question as to what your purpose was, to see if you could do direct burial.
I understand that you would run a conduit for 11 conductors; direct burial would not likely be a good choice here. Have you figured generously for voltage drop? You don't want the combination of running loads and inrush current draws to bog down that generator.
active1
10-03-2009, 03:42 PM
I will be pulling (7) #8's and (4) #12's in it. It is an 8kw generator.
Why so many # 8's?
What is it a 1ph and your planing on putting the transfer switch on the gen?
If so I would sugest putting the transfer switch on the building. Also upsizing to 3 #6 and 1 #8 ground.
I would upsize to 1 1/4" and / or run the control wires in a 3/4. Not much difference in price changing 1 PVC size.
laketime
10-03-2009, 04:56 PM
The generator requires (3) #10's I am up sizing to #8's
The pump requires (2) #10's I am up sizing to #8's plus a ground and the running the (4) control wires in #12's