Mr. Wizard
10-03-2009, 02:45 PM
I'm trying to find, and probably overlooked, requirements and distances that allow an meterbase to be installed near a natural gas meter. This install is residential, and the customer wants the meterbase moved from the back of the house, where they are going to add a room, to around the side of the house where the gas meter is located. Thanks
mcclary's electrical
10-03-2009, 02:52 PM
I'm trying to find, and probably overlooked, requirements and distances that allow an meterbase to be installed near a natural gas meter. This install is residential, and the customer wants the meterbase moved from the back of the house, where they are going to add a room, to around the side of the house where the gas meter is located. Thanks
In VA. The meter alone would not pose a problem. But if there's an ocpd, the distance would be 10 feet from the gas meter (if the gas meter vents to atmosphere) most do, and if it doesn't vent to atmosphere, the nearest OCPD can be 3 feet. These are gas regs, not NEC. Son no vent, 3 feet, vent 10 feet to ocpd.
iMuse97
10-03-2009, 04:31 PM
What MAC said. Call your gas co. and they will let you know what's up.
Power Tech
10-03-2009, 04:33 PM
I'm trying to find, and probably overlooked, requirements and distances that allow an meterbase to be installed near a natural gas meter. This install is residential, and the customer wants the meterbase moved from the back of the house, where they are going to add a room, to around the side of the house where the gas meter is located. Thanks
Here, 10" from a corner and window to the center of the meter. 24' from where the gas comes into the house counting the gas meter. On the other side of the gas meter it is 10" from the center of the meter.
Of corse specs very, and your requirements may be different, get a book or go online to your local POCO or gas co.
Kdog76
10-03-2009, 07:55 PM
Around here, the local electrical utility (POCO) has its own regulations. I believe most utilities provide electrical regulations on service equipment. Here in Alliant Energy's territory (a local utility for WI) they state 3' clearance from the gas relief valve of the gas meter to the electrical meter. My advice, obtain the reg's of the local utility, or talk to the local engineer. POCO's engineer's are usually pretty good to get info on clearance issues. I have both sets of reg's on my truck AND the utility company's engineers on my phone's contacts. Above & beyond the NEC, I believe...(but don't quote me:grin:)
Kdog76
10-03-2009, 08:00 PM
What MAC said. Call your gas co. and they will let you know what's up.
I believe it's not so much a gas utility issue as it a local POCO issue.
GUNNING
10-03-2009, 08:16 PM
Here its 3 feet from a gas meter but there is a utility regulation where all utilities must be within 3 feet of the service entrance (CATV, Phone) so that they can be on the common bond. However, the gas is not to be bonded.
ivsenroute
10-03-2009, 09:05 PM
PPL in PA is 3' horizontal from natural gas and 10' from propane
Charlie Bob
10-03-2009, 11:08 PM
Service upgrade jobs depend a lot on what you got to play with, so around here poco don't get to picky on that. I've had them withing 3' from gas meter before.
okeefe
10-03-2009, 11:16 PM
Around here the power company will send out a planner and tell us where the meter can be relocated. I would talk to them first before I installed it