View Full Version : Wiring motion detectors in parallel


FrancisDoody
11-15-2009, 11:14 AM
Have a job requirement to wire R.A.B. model STL-110 motion detectors in parallel. Is this possible and will it be reliable. Thanks.

Dennis Alwon
11-15-2009, 11:27 AM
Have a job requirement to wire R.A.B. model STL-110 motion detectors in parallel. Is this possible and will it be reliable. Thanks.
Not sure what you want to do but I have wired two standard motion detectors that control one set of lights. Basically you feed one motion and then run a 3 wire to the 2nd motion. From there go to your lights (Load). It is the same as you would wire a 3 way switch to some degree. Feed your black wire of the 3 wire cable and energize both smokes then the reds get connected together and tied to the load.

Does this help

Rewire
11-15-2009, 12:03 PM
Not sure what you want to do but I have wired two standard motion detectors that control one set of lights. Basically you feed one motion and then run a 3 wire to the 2nd motion. From there go to your lights (Load). It is the same as you would wire a 3 way switch to some degree. Feed your black wire of the 3 wire cable and energize both smokes then the reds get connected together and tied to the load.

Does this help

we have done this on long driveways nto control the lights along the driveway from either end

Dennis Alwon
11-15-2009, 12:53 PM
we have done this on long driveways nto control the lights along the driveway from either end

Moi Aussie (me also) and it works very well.

sparks2000
11-15-2009, 01:43 PM
Not sure what you want to do but I have wired two standard motion detectors that control one set of lights. Basically you feed one motion and then run a 3 wire to the 2nd motion. From there go to your lights (Load). It is the same as you would wire a 3 way switch to some degree. Feed your black wire of the 3 wire cable and energize both smokes then the reds get connected together and tied to the load.

Does this help

What do you mean by ENERGIZE BOTH SMOKES? Why did you say SMOKES?

augie47
11-15-2009, 01:47 PM
check the rating of the motion detectors. when only 1 activates it will have to carry the full lighting load. Some of them have pretty low ratrings.

Dennis Alwon
11-15-2009, 01:48 PM
What do you mean by ENERGIZE BOTH SMOKES? Why did you say SMOKES? I meant motion detectors. Power both units with the black and feed the red thu to the load connecting both red wires together of the motion detectors

sparks2000
11-15-2009, 02:04 PM
ok! makes sence, but are those motion sensors capable of handling that much of a load?

Rewire
11-15-2009, 02:30 PM
ok! makes sence, but are those motion sensors capable of handling that much of a load?

you can order 1500w detectors

sparks2000
11-15-2009, 02:45 PM
oh ok! Good to know, thanks! I'm glad I found this website,lots of good info!

LarryFine
11-15-2009, 09:54 PM
ok! makes sence, but are those motion sensors capable of handling that much of a load?
If not, have them activate a contactor.

goldstar
11-15-2009, 11:08 PM
Probably can without a problem but I would contact RAB just to make sure. They're in Northvale, NJ