6-64 Log #2312 NEC-P06 Final Action: Reject
(310.15(B)(2)(a), Exception No. 6)
_______________________________________________________________
Submitter: Mike Green, Municipality of Anchorage
Recommendation: Add Exception No. 6 to read as follows:
Exception No. 6: Where the load is divided among multiple conductors of the same circuit and phase supplying different loads, they shall be permitted to be counted as one conductor for derating purposes where all of the conductors are
identified by circuit.
Substantiation: This proposal is based on the same principal that allows the neutral of single phase multi-wire branch circuits to be ignored when counting current carrying conductors. Since the heat produced in a conductor is the square of the current, the total heat will always be reduced when the current is divided among multiple conductors. Requiring the conductors to be identified by circuit is necessary to verify the proper application of the exception.
Luminaires have become so efficient that dozens of them can be supplied by a single 20 amp branch circuit and new energy codes will require more appropriate control of individual areas resulting in control panels with many switch legs from the same circuit. This exception will reduce the unnecessary oversizing of conductors in raceways connected to those panels and to enclosures with multiple switches.
Panel Meeting Action: Reject
Panel Statement: The panel does not agree with the submitter’s substantiation. There was no evidence of any need or problem addressed by the substantiation. Conductors connected to the same circuit and supplying different loads are, in fact, current-carrying conductors and need to be counted when applying 310.15(B)(2)(a).
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11