mb5412
08-26-2004, 02:51 PM
I'm trying to get an understanding of the code as it pertains to the use of outdoor service disconnects.

If it's installed outdoors(service disconnects)
at the meter can I locate the loadcenter indoors w/o regard to distance from the point of entrance of the feeder?

If the code allows this, does this mean that a 4conductor feeder is to be run to the loadcenter?(2hots, 1neutral, 1grounding) and the outdoor service disconnect is to be grounded and bonded?

Philadelphia Pa, S. Jersey area.

Thanks

electricman2
08-26-2004, 03:38 PM
can I locate the loadcenter indoors w/o regard to distance from the point of entrance of the feeder?
Yes
does this mean that a 4conductor feeder is to be run to the loadcenter?(2hots, 1neutral, 1grounding) and the outdoor service disconnect is to be grounded and bonded?
Yes

charlie b
08-26-2004, 04:57 PM
Washington State has an administrative code that would limit you to fifteen feet (i.e., maximum distance within the building before hitting a disconnecting means). If you run the conduit in a concrete duct, or under the slab, then the fifteen foot limit does not begin until the conduit comes up from the concrete.