Can I staple NM cable to the bottom of the TGI's in a crawl space or do I have to Bore holes. I know in a basement I have to drill unless it is 2-#6 or 3--#8
[ February 20, 2003, 04:39 PM: Message edited by: myyz250 ]
jxofaltrds
02-20-2003, 07:01 PM
Through the joists.
Mike P.
rick5280
02-20-2003, 07:17 PM
It's also ok to attach to running boards. See Article 334.15(C) for details. Through the prepunched holes in TGIs are alot easier than installing running boards.
Rick Miell
chris white
02-22-2003, 04:40 PM
If you're only running a couple cables, a sharp 3/4" paddle bit blasts through those TJI webs pretty quickly with a battery drill. The prepunched holes almost never line up.
scott
02-25-2003, 08:10 PM
I have a different point of view for crawl spaces only...
You do not need running boards for NM in a crawl space. You also do not need to drill or punch throuhg the TGI's in a crawl space. Stapling directly to the bottom of the TGI is perfectly acceptable in a crawl space.
Most TGI's have specific rules from the manufacturer and by building code allowing placement of non pre-punched holes in TGI's. In other words, drilling your own hole may weaken the TGI, and is generally frowned upon.
I would recommend stapling to the bottom - fastest, safest, yet still code compliant method.
Please note that this view is shared by all of the AHJ's that I have ever worked with. This view may not be the case in your neck of the woods, so I would check with your AHJ.
Enjoy your day!