View Full Version : K-13 rated transformer grounding electrode conductor


fredw
03-24-2003, 11:02 AM
If you have a K-13 rated transformer that serves a 120/208V panelboard with a 200% rated neutral, does the grounding electrode conductor need to be increased 200%?

ron
03-24-2003, 12:30 PM
Although an equipment grounding conductor is increased based on volt drop, it nor a GEC gets increased due to potential hamonic content.

dereckbc
03-24-2003, 01:15 PM
No. A K rated transformer establishes a rating method to indicate thier ability for nonsinusodial load currents without exceeding thier tempature rise limits. The GEC and EGC's do not carry any load currents