In regards to Class 2 and Class 3 circuits, is 725-52
allowing open air splices and not required to be in a j-box? Or can chapter 3 requirments be inforced as well?
mikeackley
03-05-2003, 04:21 PM
Boxes not required for Class 2 or 3 splices or connection points providing it's not fire alarm. And providing it's not in a fire rated wall, floor, or ceiling [300-21].
Data Source: Mike Holt's Illustrated Guide to Low Voltage and Limited Energy, Unit 7, General Wiring Requirements.