captklutz
09-28-2003, 08:10 PM
Need some advice here. I install temp control systems and have an engineer that wants the secondary side of the x-former to be fused. reading the code about x-formers, class 2 is such that it is inherently(sp?) protected. I could not find anything about fusing such x-former.
What I have is a x-former, 24 volt. each wire will have 12 volts unless you ground one leg then you have 24v to ground. Our installation practice is not to ground any of the legs and we set on 50VA x-former for the controller and a 96VA x-former to power the controlled devices.
On the 50VA x-former, no legs are to be grounded. On the 96VA we can ground one leg to remove noise that the sensors get from some acuators we use. I will not go into detail on this part.
So I am thinking that by code all ungrounded conductors need to be fused. Thus I feel I would need 3 fuses min. 4 at the most.
Am I correct in my thinking? I have argued my thoughts with my co-workers who insist on just putting one fuse for each transformer grounded or not.
Thanks!
What I have is a x-former, 24 volt. each wire will have 12 volts unless you ground one leg then you have 24v to ground. Our installation practice is not to ground any of the legs and we set on 50VA x-former for the controller and a 96VA x-former to power the controlled devices.
On the 50VA x-former, no legs are to be grounded. On the 96VA we can ground one leg to remove noise that the sensors get from some acuators we use. I will not go into detail on this part.
So I am thinking that by code all ungrounded conductors need to be fused. Thus I feel I would need 3 fuses min. 4 at the most.
Am I correct in my thinking? I have argued my thoughts with my co-workers who insist on just putting one fuse for each transformer grounded or not.
Thanks!