View Full Version : low voltage cable sizing
txturbo
07-28-2003, 02:37 PM
What size cable do I need for 12V 750 amps? Its just a short run of about 4 feet.
tom baker
07-28-2003, 03:17 PM
Is this for winch? Check the instructions that came with it.
txturbo
07-28-2003, 04:42 PM
No.....its for the output of a electroplating rectifier.I need to connect the output buss bars to the buss bars at my plating bench.
iwire
07-28-2003, 06:52 PM
txturbo, amps are amps regardless of the voltage, you will need to run parallel conductors to get 750 amp capacity.
Something like 3 sets of 250 kcmil, or 2 sets of 500 kcmil will do it if your terminations are rated 75C and you use 75C wire.
txturbo
07-28-2003, 07:12 PM
Thanks iwire. Thats what I was looking for.
bennie
07-28-2003, 08:04 PM
Four feet can be a mile to 12 volts. Be sure you use the figures Bob has given, plus a little more.
You will notice when maximum current is flowing in your plating tanks, the voltage will read zero on convential volt meters. Resistance is the principal concern. The lower the resistance the more available current. Heating effects are negligible due to low (eye two are).