Do you know if exist a table that supply the Nm value that the Electricians must to apply to the screw, to avoid Hot points.

bphgravity
03-31-2003, 02:18 PM
If you are talking about proper terminal torquing, then the specific value will be listed and labeled for the respective device or equipment from the manufacturuer. There is not a standard value or table that I am aware of.

Ed MacLaren
03-31-2003, 10:08 PM
There is a table of tightening torques for various types and sizes of terminal screws/lugs in the Canadian Electrical Code, but the torque ratings are given in lbs-inches, not newton-meters (Nm).

Ed

fallssparky
04-01-2003, 08:02 AM
In the 2003 code hand book there is a table on page 45, actually starts on page 44 under 110.14
Electrical Connections.
The downside is it is in #-in not Newton-meters/N-m.

sparky

charlie b
04-01-2003, 10:24 AM
Multiply the pound-inch value by 0.113 to get the value in newton-meters.