View Full Version : Emergency Exit circuit


elliselectric
04-24-2003, 08:04 PM
Where, and in what code, is it permissible to supply exit, and emergency lighting from the local lighting circuit ahead of the light switch?

roger
04-24-2003, 08:44 PM
As far as The NEC, you can look at700.12(E).
There is more information in NFPA 101

Roger

elliselectric
04-24-2003, 11:15 PM
That's the one. Thanks Roger

doug glasscock
04-29-2003, 12:15 PM
I have read 700-12 (twice) and I don't see it but would like to.
Could you be a little more specific as to where and what year CODE. I am looking in 99'.

iwire
04-29-2003, 04:28 PM
Doug, This is the same in the 1999 code.

700.12(e) Unit Equipment

It is in the last paragraph, also read the exception.

[ April 29, 2003, 04:28 PM: Message edited by: iwire ]

doug glasscock
05-01-2003, 04:33 PM
Thanks Iwire, got it