PDA

View Full Version : 250.96(B)


ryan_618
05-11-2005, 09:23 PM
B) Isolated Grounding Circuits. Where delete "required" required for the reduction of electrical noise (electromagnetic interference) on the grounding circuit, an equipment enclosure supplied by a branch circuit shall be permitted to be isolated from a raceway containing circuits supplying only that equipment by one or more listed nonmetallic raceway fittings located at the point of attachment of the raceway to the equipment enclosure. The metal raceway shall comply with provisions of this article and shall be supplemented by an internal insulated equipment grounding conductor installed in accordance with 250.146(D) to ground the equipment enclosure.

Change to read:


B) Isolated Grounding Circuits. Where installed for the reduction of electrical noise (electromagnetic interference) on the grounding circuit, an equipment enclosure supplied by a branch circuit shall be permitted to be isolated from a raceway containing circuits supplying only that equipment by one or more listed nonmetallic raceway fittings located at the point of attachment of the raceway to the equipment enclosure. The metal raceway shall comply with provisions of this article and shall be supplemented by an internal insulated equipment grounding conductor installed in accordance with 250.146(D) to ground the equipment enclosure.

Substantiation:

Generally speaking, isolated ground circuits are not required to be installed. When they are installed it is because of a designers inclination, not a code or manufacturer’s requirement. This section must be changed to reflect that fact.

charlie
05-11-2005, 09:48 PM
This looks like a slam dunk. :D

George Stolz
05-11-2005, 09:50 PM
Looks good! :)

ryan_618
05-11-2005, 09:53 PM
Thanks guys :)