elmarea
10-31-2005, 08:04 PM
I'm a controls technician for a Natural Gas Utility. We're wiring devices in a C1D1 location.
The company lost its experienced technician who used to do all the hazardous location wiring. I've been asked to wire this device and use his previous installations as an example. I have no engineering support on this job.
The trouble arises when I get to the terminations. The devices are temp and pressure xdcrs rated for the location. (C1D1 XP) Rigid steel conduit with 2 conductor shielded cable.
I'm saying sealing at the device is required per Art 501.5 (D), (working from memory code bk at work) plus Mike Holt's guide on special occupancies, but the previous technician neither sealed the cable at the device end nor the terminations at the cable ends.
Is sealing of the cable and terminations at the device end required? What products do you use to seal if required?
Thanks
The company lost its experienced technician who used to do all the hazardous location wiring. I've been asked to wire this device and use his previous installations as an example. I have no engineering support on this job.
The trouble arises when I get to the terminations. The devices are temp and pressure xdcrs rated for the location. (C1D1 XP) Rigid steel conduit with 2 conductor shielded cable.
I'm saying sealing at the device is required per Art 501.5 (D), (working from memory code bk at work) plus Mike Holt's guide on special occupancies, but the previous technician neither sealed the cable at the device end nor the terminations at the cable ends.
Is sealing of the cable and terminations at the device end required? What products do you use to seal if required?
Thanks