We are installing a day tank for diesel fuel in an enclosed CMU constructed room, located outside in a parking lot. Does any or all of the exposed conduit and fittings require classifcation?

rbalex
07-28-2005, 07:50 PM
See this thread. (http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=22;t=000043)

petersonra
07-30-2005, 08:59 AM
Originally posted by pmc:
We are installing a day tank for diesel fuel in an enclosed CMU constructed room, located outside in a parking lot. Does any or all of the exposed conduit and fittings require classifcation? just to clarify what might be a bit of a misconception.

conduit and fittings are not classified. classification refers to the geographic area in which you might install them and indicates there is a specific risk of fire that requires special precautions be taken to reduce that risk.

conduit and fittings may either be identified in the code or listed by a testing agency as suitable for use in an area that is classified.

ryan_618
07-30-2005, 09:10 AM
Thats a great point Bob.