View Full Version : Bundled MC
Do inspectors turn down installation of more than three MC cables bundled together? Such as home runs installed in drop ceiling going to the same area. cables are zip-tied together. Why does 310.15 (B)(2)(a) exception No 5 specify conductors to be number 12 awg? Why not 10 awg or 8 awg? What does exception number 5 mean by "Type MC cable without an overall outer jacket"?
PS sorry I should have put this in the NEC section
George Stolz
10-25-2006, 08:09 PM
See 310.15(B)(2)(a), exception 5. MC cables on bridle rings are considered bundled.
However, that does not make it illegal - it just means you would have to derate the cables, and be sure that your ampacity is not less than the OCPD protecting it.
Off the record, ;) , I would question how close together you were running those cables. Were they zip-tied together tightly, or did they simply run side by side?
jjhoward
10-25-2006, 08:19 PM
How about modular homes that place plastic conduit in the walls for dropping in the bundles of wires from the attic to the basement?
I have seen that in 4 modular homes, and the inspector has yet to flag it.
The wire capacity (OCPD) has not been reduced. 12 awg wires all had 20 amp breakers in the breaker pane.
infinity
10-25-2006, 08:22 PM
There is an exception that allows up to 20 #12 AWG CCC's bundled together to be derated to 60%. For 20 CCC's this would work to a derated ampacity of 18 amps (30amps X 60%) so these circuits could be protected by a 20 amp CB. You just have to be careful when applying the provisions of 240.4(B). Multi-receptacle circuits can not be rounded up to the next higher standard OCPD device.
See 310.15(B)(2)(a), exception 5. MC cables on bridle rings are considered bundled.
However, that does not make it illegal - it just means you would have to derate the cables, and be sure that your ampacity is not less than the OCPD protecting it.
Off the record, ;) , I would question how close together you were running those cables. Were they zip-tied together tightly, or did they simply run side by side?
Why does exception No 5 specify conductors to be number 12 awg? Why not 10 awg or 8 awg? What does exception number 5 mean by "Type MC cable without an overall outer jacket"?
jjhoward
10-25-2006, 08:38 PM
These 20 amp circuits were all general purpose lighting/power circuits. Seems like they should be derated.
GUNNING
10-27-2006, 11:08 PM
Its that 5 degree Celsius rise in temperature from all those wires being bundled together. It just ruins all those screws on those switches and outlets and breakers. I wonder what the engineers would do if they found out about the 100 degree Celsius summer temperatures in attics all across the country. Shshshsh. I guess that would be 205 degrees if the wires were bundled more than 5 together. I hope the copper industry doesn't here about this or they will have us run 8-2 w/ grds for 20 amp circuits, in conduit.