Can some one print out the page from the NEC Section 800 that shows that Abandon Cable cannot be left in cieling???

Removed email

roger
02-14-2007, 06:02 PM
What year NEC do you own?

Roger

don_resqcapt19
02-14-2007, 06:05 PM
800.2 ... Abandoned Communications Cable. Installed communications cable that is not terminated at both ends at a connector or other equipment and not identified for future use with a tag.
800.3(C) (C) Spread of Fire or Products of Combustion Section 300.21 shall apply. The accessible portion of abandoned communications cables shall not be permitted to remain.
So the key is if you don't want to remove it you just tag it for future use and then it poses no danger.
Don

peter d
02-14-2007, 07:26 PM
So the key is if you don't want to remove it you just tag it for future use and then it poses no danger.
Don

Right, just like the electrons behaving differently on the load side of the service disconnect.

LarryFine
02-14-2007, 09:14 PM
How do it know? :-?