View Full Version : Minimum rating of disconnect for remote building


COELECTRIC
04-05-2007, 12:58 PM
I am unclear if there is a minimum rating for a branch circuit serving a panel board in a remote building. I understand for a SERVICE disconnect with more than two circuits, the minimum is 60A.

I have a customer who is planning to build a 30'x40' workshop adjacent to his house. Minimal loads, mostly lighting and general receptacles. Client requested a seperate panel board in workshop.

Thanks in advance.

don_resqcapt19
04-05-2007, 01:20 PM
Take a look at 225.39.
Don

COELECTRIC
04-05-2007, 01:28 PM
Perfect...
Thank you - Don.