I work for a wind turbine company doing mid size turbine installs on farms or industrial properties. A big deal for many of these projects is dealing with the long runs between the turbines and the existing service.
Traditionally if I was doing work where I had to get power 1000-2000 feet from existing power, it would be time to talk to the power company and get a new service put in near the new load. But we have the unique requirement that since we're offsetting the customer's load, we must be tying into the customer's panel where we will be downstream from the utility meter.
I'm wondering if someone here has experience / advice at looking at installing step up and step down pad mount transformers for the runs? Any idea where the cost break-over would be?
In most cases the power level is around 50kW to 120kW. On our end of the equipment we can connect at either 240V or 480V. So far we've done a few where fortunately the customer had 480V and then the run is more reasonable. But now we are looking at several where the farm has 240V delta.. and 50+ kW going 1000+ feet gets beyond nuts for the wire.
Traditionally if I was doing work where I had to get power 1000-2000 feet from existing power, it would be time to talk to the power company and get a new service put in near the new load. But we have the unique requirement that since we're offsetting the customer's load, we must be tying into the customer's panel where we will be downstream from the utility meter.
I'm wondering if someone here has experience / advice at looking at installing step up and step down pad mount transformers for the runs? Any idea where the cost break-over would be?
In most cases the power level is around 50kW to 120kW. On our end of the equipment we can connect at either 240V or 480V. So far we've done a few where fortunately the customer had 480V and then the run is more reasonable. But now we are looking at several where the farm has 240V delta.. and 50+ kW going 1000+ feet gets beyond nuts for the wire.