View Full Version : Pool Question
Energized77
05-29-2007, 08:11 PM
Does it say I need a dedicated branch circuit for my pool pump?
Can I GFCI protect my pool pump 20Amp twistlock outlet with the required GFCI outlet located no closer than 10, but no farther than 20 feet from the inside of the pool wall?
tmbrk
05-29-2007, 08:19 PM
Your pool pump 20amp twist lock receptacle must be on its own dedicated GFCI protected circuit. The GFCI convenience receptacle between 10 and 20 feet from the inside wall of the pool does not have to be dedicated.
stickboy1375
05-29-2007, 08:29 PM
Your pool pump 20amp twist lock receptacle must be on its own dedicated GFCI protected circuit. The GFCI convenience receptacle between 10 and 20 feet from the inside wall of the pool does not have to be dedicated.
Can I have a code article with that statement..?
tmbrk
05-29-2007, 09:09 PM
I don't know if there is an article that pertains to this directly, but I personally have never seen a pool pump where the manufacturer does not require a dedicated circuit.
stickboy1375
05-29-2007, 09:12 PM
One more thing, if your receptacle for Circulation and Sanitation is MORE than 10' twist-lok receptacles are not required.
Energized77
05-29-2007, 10:38 PM
One more thing, if your receptacle for Circulation and Sanitation is MORE than 10' twist-lok receptacles are not required.
I watched the Mastering the NEC 2005 section on article 680 and Mark Shapiro said it is typical to GFCI protect the 20Amp twistlock receptacle for the pump from the load side of the general purpose GFCI receptacle.
I did an installation this way and got reamed by the inspector who told me I need to review my article 680. I find nothing to the contrary. Any help??
Dennis Alwon
05-29-2007, 11:00 PM
If the motor draws more than 50% of the circuit than you must put it on a dedicated cir. Art. 210.23 (A)(2)
bradleyelectric
05-29-2007, 11:10 PM
duplicatepost
stickboy1375
05-30-2007, 07:25 AM
If the motor draws more than 50% of the circuit than you must put it on a dedicated cir. Art. 210.23 (A)(2)
Dennis, I don't believe pool pumps are fastened in place, at least not in the New England...:D
stickboy1375
05-30-2007, 07:29 AM
I watched the Mastering the NEC 2005 section on article 680 and Mark Shapiro said it is typical to GFCI protect the 20Amp twistlock receptacle for the pump from the load side of the general purpose GFCI receptacle.
I did an installation this way and got reamed by the inspector who told me I need to review my article 680. I find nothing to the contrary. Any help??
What part don't you understand? The twist-lok requirement? or the GFI Requirement?
Energized77
05-30-2007, 07:40 AM
I don't understand the required means for GFCI protecting my 20Amp twistlock. Why can't I run a circuit from the panel to my required GFCI outlet no more than 20 but no less than 10 feet from my pool and load side protect my 20 Amp twistlock outlet for the pump? Can I if the pump doesn't draw 50% or more of the circuit ampacity?
guschash
05-30-2007, 07:44 AM
Atricle 680.22(5) Receptacles that supply pool pump motors, shall be provided with GFCI protection.
Dennis Alwon
05-30-2007, 07:55 AM
Dennis, I don't believe pool pumps are fastened in place, at least not in the New England...:D
Interesting-- a disposal is fastened in place but a pool pump is not even though the circulation lines are attached to it.
Dennis Alwon
05-30-2007, 07:58 AM
I don't understand the required means for GFCI protecting my 20Amp twistlock. Why can't I run a circuit from the panel to my required GFCI outlet no more than 20 but no less than 10 feet from my pool and load side protect my 20 Amp twistlock outlet for the pump? Can I if the pump doesn't draw 50% or more of the circuit ampacity?
I would say yes but I doubt that this is the case unless this is an above ground pool. I would ask the AHJ what article he is quoting.
stickboy1375
05-30-2007, 05:55 PM
Interesting-- a disposal is fastened in place but a pool pump is not even though the circulation lines are attached to it.
Dennis, so if the pump was piped in with unions and required no tools to relocate the pump would you consider that fastened in place?
Dennis Alwon
05-30-2007, 06:00 PM
Dennis, so if the pump was piped in with unions and required no tools to relocate the pump would you consider that fastened in place?
I would consider it fastened in place but that don't mean a thing. I figure if you can unplug it and move it then it is not fastened into place. -- a disposal doesn't need any tools to disconnect it.
stickboy1375
05-30-2007, 06:08 PM
I would consider it fastened in place but that don't mean a thing. I figure if you can unplug it and move it then it is not fastened into place. -- a disposal doesn't need any tools to disconnect it.
Yeh, I see your point, I was just curios as to why the OP failed...
electricmanscott
05-30-2007, 09:21 PM
Back to one of the questions asked somewhere along the way. The required receptacle (not the one for the pump) must be fed from a general purpose branch circuit. Would a circuit that fed the pump and the required recept be considered a general purpose branch circuit?
I tend to think not. In my mind by putting that requirement in there they are saying in a way only the NEC can, that you can't use the pump circuit for the required convenience outlet.
vBulletin® v3.7.3, Copyright ©2000-2009, Jelsoft Enterprises Ltd.