I need to find a pop up for required counter receptacles in a kitchen remodel.
Mockit has a 15 amp but I can't seem to find a 20 amp one that would be suitable for a kitchen counter top. I would need 3.

infinity
08-08-2007, 05:45 AM
Is the Mockit 15 amp a duplex or a single receptacle? A 15 duplex is all that's required.

Fault Finder
08-08-2007, 05:50 AM
Even if it is going to be on a 20 amp GFI breaker?

Dennis Alwon
08-08-2007, 06:28 AM
Even if it is going to be on a 20 amp GFI breaker?


Kitchen receptacles and gfci receptacles don't need to be 20 amp devices. 15 amp recep. is all that is needed nless it is an individual circuit with a single receptacle. Read art. 210.21(B)(1) then read Table 210.21(B)(3)

LarryFine
08-08-2007, 10:39 AM
Even if it is going to be on a 20 amp GFI breaker?Even if. A 15a receptacle has the same electrical capacity as a 20a receptacle. The only difference is the slot shape.

. . . an individual circuit with a single receptacle.Note to F.F.: One duplex receptacle is not a single receptacle, it is two receptacles.

360Youth
08-08-2007, 11:42 AM
I just posted this a few days ago. Check out the opinions and links.

http://forums.mikeholt.com/showthread.php?t=89135

Fault Finder
08-09-2007, 05:17 AM
Thank you all for taking the time to contribute. The wealth of experience is priceless to have access to.

e57
08-09-2007, 10:21 PM
Where in the code does it say you can have the 210.52(C)(1) through (5)outlets be an outlet strip/extention cord? :rolleyes: The whole point of this code is not to use extention cords... The oulets that are supposed to be installed in those locations are to be fed by a 20a circuit. IMO if the outlet that is popping up to cover the location - it should be hard-wired, and/or rated at 20a right up to that location even if it is a 5-15. Not from a 16ga extention cord to the 20a circuit below.

FYI I am sick of these things....

Dennis Alwon
08-09-2007, 11:14 PM
These units are hard wired.