View Full Version : Help in determining service calculation.
stever1971
08-20-2007, 03:06 PM
I am looking for some help in determing service size for 16 unit assisted care facility. 13,579 square feet, 192 amp air conditioning load, 4 washing machines, each unit will be equipped with a microwave at approx. 1000 watts, each units lighting load will not exceed 11 amps, the commen areas lighting load is 121 amps.
haskindm
08-20-2007, 04:14 PM
Follow the steps in article 220.
You have most of the information that you need. Lighting load will be based on the square footage. Is there any heating load?
If you still have questions, post your attempt at a calculation and I am sure members here will let you know if you made any mistakes.