View Full Version : VFD drive cable
bhall1
12-31-2007, 05:57 PM
What is the proper way of terminating VFD drive cable? Can the braided shield be trimmed back with the rest of the outer insulation/jacket.
cbranter
12-31-2007, 09:51 PM
what ty[e of cable are you describing?
ESP HV cable has special connectors where it exits the well casing
benaround
12-31-2007, 11:11 PM
bhall1,
The shield is usually grounded at the supply end, manafactures instructions
should be followed in any case.
iwire
01-01-2008, 05:45 AM
I agree with Frank, you bond the shield to ground on the supply end and isolate it at the other end.
vBulletin® v3.7.3, Copyright ©2000-2009, Jelsoft Enterprises Ltd.