View Full Version : Fire Alarm AC Connection
Hello, and thank you for your help.
I am about to install several fire alarm panels monitoring waterflow and gate valves.
The riser rooms are a controlled location and only accessible by authorized personell. Each riser room as a regular AC plug that is on a dedicated circuit. Can I just plug the fire panel into these plugs, or must the fire panel be hardwired to the AC lines?
This is in Utah.
Thanks for the help.
Fire Alarm
01-25-2008, 06:49 PM
It must be hardwired.
MichaelGP3
01-25-2008, 08:52 PM
It must be hardwired.
......to a 20 amp circuit breaker (on an emergency panel, if emergency power is present at the facility in question).
480sparky
01-25-2008, 09:04 PM
......to a 20 amp circuit breaker (on an emergency panel, if emergency power is present at the facility in question).
And typically with a breaker lock on it.
And if no emergency power is present? NFPA 72 1-5.2.3 calls for two power supplies, in my case the primary being commercial AC, and secondary being battery backup. 1-5.2.5.2 calls for the connection to be "mechanically protected".
I kinda assume it should be hardwired, but I can't see in the code where that is required? Is it up to the AHJ?
MichaelGP3
01-25-2008, 09:31 PM
NFPA 72 1-5.2.5.1(b) states ".....having a continuous unfused neutral conductor". A plug and outlet doesn't meet the definition of 'continuous'.
Gottcha...I didn't catch that the first time around. Makes sense.
Thanks everyone.
Fire Alarm
01-25-2008, 09:55 PM
NFPA 72 1-5.2.5.1(b) states ".....having a continuous unfused neutral conductor". A plug and outlet doesn't meet the definition of 'continuous'.
Damn! You're good!
DUCKMAN
01-26-2008, 03:28 PM
And typically with a breaker lock on it.
I do not see where a breaker lock is requred. The breaker must be marked, and the circuit must be mechanically protected, but I do not see a requirement for a breaker lock anywhere. I hear this often, but have yet to see it anywhere in the code.
peter d
01-26-2008, 05:39 PM
The breaker must be marked, and the circuit must be mechanically protected, but I do not see a requirement for a breaker lock anywhere. I hear this often, but have yet to see it anywhere in the code.
You're right, it's not an NFPA 72 requirement. It's a local code in my area.
So what would you make of 1-5.2.5.2 "...Circuit disconnecting means shall have a red marking, shall be accessible only to authorized personnel, and shall be labeled as FIRE ALARM CONTROL."
(Bold added for emphasis)
It seems that some could interpret that to be a lock of some sort, maybe on the whole panel?
I've just started working on my NICET 1 certs (meaning I'm a newbie to fire), so I'm not trying to start an argument, just trying to learn...
DUCKMAN
01-27-2008, 10:12 AM
So what would you make of 1-5.2.5.2 "...Circuit disconnecting means shall have a red marking, shall be accessible only to authorized personnel, and shall be labeled as FIRE ALARM CONTROL."
(Bold added for emphasis)
It seems that some could interpret that to be a lock of some sort, maybe on the whole panel?
I've just started working on my NICET 1 certs (meaning I'm a newbie to fire), so I'm not trying to start an argument, just trying to learn...
A breaker lock does not prohibit unauthorized personel from shutting off the power. I believe that the intent is that the panel is either locked, or in a locked room.
iwire
01-27-2008, 11:09 AM
A breaker lock does not prohibit unauthorized personel from shutting off the power. I believe that the intent is that the panel is either locked, or in a locked room.
In my opinion a breaker lock is as effective as a locked panel.....in other words....either is easily defeated.
It's much over nothing considering the AC power is supervised by the fire panel anyway.
Fire Alarm
01-27-2008, 01:09 PM
I've just started working on my NICET 1 certs (meaning I'm a newbie to fire), so I'm not trying to start an argument, just trying to learn...
Be aware that NICET is currently overhauling their certs and are about to roll out a substantially changed testing format.
Be aware that NICET is currently overhauling their certs and are about to roll out a substantially changed testing format.
Do you know when the new format will be taking effect? I plan on testing in May, so hopefully what I have been studying will still be fairly in line with the test....
Thanks for the heads up.