02-06-2008, 02:53 PM
Do Nuteral Wires Count in pipe fill ? If so were is it stated in the NEC?

roger
02-06-2008, 03:16 PM
All conductors count in conduit or tubing fill even the EGC, see chapter 9, note 3 to the Table notes.

Are you thinking about the neutral being counted for derating purposes?

Roger

infinity
02-06-2008, 04:28 PM
Think of the words that you mentioned "pipe fill". If it fills the pipe it counts for conduit fill. This would included ungrounded, grounded and grounding conductors.