Can a keyosk (non-explosion proof, with switching devices) be installed next to gas dispensers, within 8'?

petersonra
05-16-2008, 09:22 AM
Can a keyosk (non-explosion proof, with switching devices) be installed next to gas dispensers, within 8'?
gasoline?

just where are the switching devices located?

tryinghard
05-16-2008, 06:11 PM
There are contactors and relays located inside the keyosk

rbalex
05-16-2008, 09:37 PM
Since Article 514 is the ruling text, the answer is NO.

See Diagram 514.3. The kiosk mentioned in the OP would be within the 18” high, 20’ radius, Division 2 location.

In many applications general purpose equipment would be acceptable, but Section 514.7 directs you to Section 511.7 which would prohibit most of the kiosk wiring and equipment.