Per section 250.50 the bonding of all electrodes are required.
My question is if you are not using the rebar in the slab as a grounding electrode in the grounding system does it become by default of just being there an electrode and require bonding.
Thanks for your help.
My question is if you are not using the rebar in the slab...
I thought that if rebar was not present, then a minimum 20' of #4 bare copper was to be installed as the c.e.e. On a new footing/foundation installation.
no, if footing steel is not present you are not required to install 20 feet of #4 copper for a cee, but you are permitted to do so.
Chris
The general concensus seems to be that if rebar is not installed per the approved set of plans,that it is not required to be part of the grounding electrode system. I thought that if rebar was not present, then a minimum 20' of #4 bare copper was to be installed as the c.e.e. On a new footing/foundation installation.
No, if footing steel is not present you are not required to install 20 feet of #4 copper for a CEE, but you are permitted to do so.
Chris
2002 NEC = Where available
2005 NEC = Are present
2008 NEC = Are Present
Just to make sure we're all on the same page, the rule talks about rebar in the foundation, not the slab.
Wikipedia said:Shallow foundations
Main article: Shallow foundation
Shallow foundations are usually embedded a meter or so into soil. One common type is the spread footing which consists of strips or pads of concrete (or other materials) which extend below the frost line and transfer the weight from walls and columns to the soil or bedrock. Another common type is the slab-on-grade foundation where the weight of the building is transferred to the soil through a concrete slab placed at the surface.
Is a slab not a foundation?
It also says footing or slab and many times a slab has footings.
Unless there is a local amendment.
Some of the jurisdictions around here require a CCE. If there is no rebar, than a #4 cu must be installed.
I have seen a few different versions of varied codes where a CEE is conditional. i.e. not required to destroy building in order to install said CEE, and some that require a CEE even if the building is not powered.So they have a local code requiring that you install a CEE even when it's not required by the NEC?
So they have a local code requiring that you install a CEE even when it's not required by the NEC?