I'm not buying that. The neutral lead on the AFCI's goes to the neutral bus in the panel.Can't do it, I'm almost positive you have to have seperate neutrals to make trhe AFCI work
I'm not buying that. The neutral lead on the AFCI's goes to the neutral bus in the panel.Can't do it, I'm almost positive you have to have seperate neutrals to make trhe AFCI work
I'm not buying that. The neutral lead on the AFCI's goes to the neutral bus in the panel.
Seriously (Hey, it could happen!), if you've gotta divide an area's supply into more than one circuit, why not do it that way?
Okay, let's say you have six recessed lights and two ceiling fans.You have 3 lighting outlets a fan outlet, 10 receptacle outlets and 2 - 15 amp circuits to supply them ........... to me dividing it by type is poor design.
Well, of course. I always globalize. :wink: I never say always or never.All I am saying is I hate 'I always do it that way' reasons, decide based on the specific conditions.:smile:
Always!That said, I have no doubt your customers are happy with your work.
they have to be seperate. if you ground the neutral coming out of an AFCI, it trips. This proves it does something with the neutral that passes through it.
With a 14/3, you would use a 2-pole AFCI designed to share the neutral...
Yes we would if one was available that meets the 2008 NEC requirements. :smile:
As of today no one makes one, that was why the suggestion was put out to use the 14/3 as a feeder to a two circuit sub panel equipped with two single pole AFCIs and run two 2-wire cables from there.