mull982:
My Fluke 87 input impedance is 10 megohms and less than 100 pfd in parallel. My typical HP (Hewlett-Packard) instruments are 10 megohms, and unknown capacitance. Typical 10X scope probes are 10 megohms and about 10 pfd shunt capacitance.
.
What if for example our meter impedence happend to be much lower than the capacitance coupled impedence. This would then lower the open circuit voltage reading we got with our meter becasue most of the voltage would drop across the coupled impedence and have less dropped across our low impedence meter. So from this I take it that we will read a different open circuit voltage or voltage on the lifted wire depending on the impedence of the meter. This would explain why when a "wiggy" which is a low impedence meter is placed across the input with the wire connected the voltage quickly drops from 28 to 0. This is because the low meter impedence in parallel with the input impedence causes a lower overall input impedence an therefore most if not all of the voltage is dropped across the coupled capactitance and does not show up on the input module.
090211-0736 EST
In a multi-conductor cable or bunch of wires where there is one floating wire of concern (meaning no connection at either end) and other hot wires that may be connected to fairly low impedance loads and from time to time are energized from a low source impedance voltage source constitutes a varying amount of capacitive coupling to the floating wire. As a result the equivalent source voltage and composite coupling capacitance to the floating wire will change.
My guess is that the greatest coupling condition to the single floating wire occurs when all other wires are energized with the maximum voltage and the same phase. This would be the test condition to use in determining the resistance and/or capacitance to load the floating wire.
.
I tested a couple of different scenarios when I was in the field. The first scenario was with the contractor pulled in in a local condition and this yieleded the maximum voltage. This give the 28V with the wire in the input and the 80V with the wire lifted from the input.
I then tested the circuit with the control station in the off position. Therfore there was no current flow, but just voltage out to the control station. From this I saw 7.7V with the wire landed and 25V with the wire in an open circuit state.
Lastly I tested the circuit with the contorl station in the local position but no current flow energizing the starter. From this I recorded 15.8V landed on the input and 48.8V in an open circuit state.
So it appears exactly as you said. The maximum coupling occurs when multiple wires are energized and there is current flowing.
Guess the magnitude of the source voltage also will determine load voltage. If we had 480V wire in the same conduit and were part of the coupling, then we could expect much larger input, and open circuit voltages than we saw.
090211-0736 EST
I definitely recommend that in addition to any shunt resistance you use that there should be shunt capacitance.
.
Is this just to deal with harmonics and noise as you mentioned.