I believe that in the situations where multiple poles of a breaker are used in parallel, the assemblies are designed so that _all_ poles trip at the same time. For example, there was a line of residential panel-boards where 4 '100A' poles were arranged in 2 parallel pairs to provide a '200A' '2 pole' main breaker.
You could contact the panel manufacturer to find out if there is a 'listed parallel assembly' of 2 100A breakers that fits your panel.
Musing here: what defines an OCPD connected in parallel? There are many situations where OCPD are somewhat parallel with each other; I'm thinking for example of a large 'dual head' service with a tie breaker or OCPD on transformer secondaries when there are multiple transformers. If you place two OCPD in a panel, run two _separate_ feeders, but both of these feeders go to the _same_ load, are those 'parallel' for the purpose of 240.8?
-Jon
You could contact the panel manufacturer to find out if there is a 'listed parallel assembly' of 2 100A breakers that fits your panel.
Musing here: what defines an OCPD connected in parallel? There are many situations where OCPD are somewhat parallel with each other; I'm thinking for example of a large 'dual head' service with a tie breaker or OCPD on transformer secondaries when there are multiple transformers. If you place two OCPD in a panel, run two _separate_ feeders, but both of these feeders go to the _same_ load, are those 'parallel' for the purpose of 240.8?