For a 480V contactor used in a size 2 motor starter the control voltage on the coil is 120V.
If the contactor is pulled in, what would the voltage on the coil have to drop below in order for the coil to dropout? I believe I saw somewhere that the contactor would stay pulled in up to 70% of its voltage which would be about 85V. I know the coil depends on the total VA, but with a voltage drop on the coil what voltage would the coil stay pulled in unitl?
Also is there a risk of damaging a coil if operated within 10% below its rating. If a 120V coil is operated continuously at 108V is there a chace of burning up the coils? Do the coils have a +/- 10% tolerance similar to motors?
What about if you power the coil with no plunger element attached on the contactor? In other words if you pull the coil itself off and power it what would happen?
If the contactor is pulled in, what would the voltage on the coil have to drop below in order for the coil to dropout? I believe I saw somewhere that the contactor would stay pulled in up to 70% of its voltage which would be about 85V. I know the coil depends on the total VA, but with a voltage drop on the coil what voltage would the coil stay pulled in unitl?
Also is there a risk of damaging a coil if operated within 10% below its rating. If a 120V coil is operated continuously at 108V is there a chace of burning up the coils? Do the coils have a +/- 10% tolerance similar to motors?
What about if you power the coil with no plunger element attached on the contactor? In other words if you pull the coil itself off and power it what would happen?