I ran across an interesting one today. On a 30gal gas HW heater, there is a small spark that arcs between the cold water pipe and the vent pipe. I did a double-take when I saw it, but then it did it again. It is random, but relatively consistent.
I figured that someone was using the water pipes as a neutral, or perhaps a ground on some equipment with a problem. Then I noticed that the vent tied into the furnace vent and thought that maybe there was a problem with the furnace (IE: there was a voltage present on the vent due to the furnace). I was able to measure 4 volts between the cold water pipe and the vent. I was actually surprised that 4 volts would arc.
There is a very faint hum near the furnace that disappears when you bond the cold water pipe to the vent. I believe the hum is coming from the vent, it sounds like a transformer hum.
I also measure .6 amps in the cold water pipe.
I actually think at this point that there is voltage being induced onto the vent and arcing to the grounded cold water pipe, but I had to leave before I could confirm that. I get the 4 volts from the cold water pipe to the vent and also from the gas pipe to the vent. I have 0 volts from the water pipe to the gas pipe. This is why I suspect the voltage on the vent. It is also possible that the gas/water pipes are bonded well and are at the same potential. There was no visible bond however.
I suspect either wires paralleling the duct, which is pretty long (not that likely I agree). Old tube and knob wiring that has cracked insulation laying on the vent, or something similar.
Any suggestions what to check? It's been arcing long enough that the starter vent actually has a hole in it from the continued arcing.
I figured that someone was using the water pipes as a neutral, or perhaps a ground on some equipment with a problem. Then I noticed that the vent tied into the furnace vent and thought that maybe there was a problem with the furnace (IE: there was a voltage present on the vent due to the furnace). I was able to measure 4 volts between the cold water pipe and the vent. I was actually surprised that 4 volts would arc.
There is a very faint hum near the furnace that disappears when you bond the cold water pipe to the vent. I believe the hum is coming from the vent, it sounds like a transformer hum.
I also measure .6 amps in the cold water pipe.
I actually think at this point that there is voltage being induced onto the vent and arcing to the grounded cold water pipe, but I had to leave before I could confirm that. I get the 4 volts from the cold water pipe to the vent and also from the gas pipe to the vent. I have 0 volts from the water pipe to the gas pipe. This is why I suspect the voltage on the vent. It is also possible that the gas/water pipes are bonded well and are at the same potential. There was no visible bond however.
I suspect either wires paralleling the duct, which is pretty long (not that likely I agree). Old tube and knob wiring that has cracked insulation laying on the vent, or something similar.
Any suggestions what to check? It's been arcing long enough that the starter vent actually has a hole in it from the continued arcing.